Trip Switches on 1ph winch trolley

11/11/2008 12:02 AM

I have a trolley that is pulled up a 45* incline by a single phase motor and winch. There is a up and down controller at the top of the incline. To get the system certified I have to put a limit switch at the top and the bottom of the incline to stop the winch. I have had some electrical contractors working on it but they can not work it out. Surely it cant be hard but these guys have tried everything I am begining to think that it is impossible. Please help

Brock

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#1

Re: Trip Switches on 1ph winch trolley

11/11/2008 12:57 AM

If there is a motor starter or contactor that runs the motor then--

Put a normally closed limit switch that will open when the the trolley hits the high point, the switch is tripped and the contacts open that are in series with the control power for the up circuit. With the contacts open, there is no way to run the motor up.

Put a normally closed limit switch that will open when the trolley hits the low point, the switch is tripped and the contacts open that are in series with the control power for the down circuit. With the contacts open, there is no way to run the motor down.

If the circuits carry the motor current, the limit switch contacts will have to be sized to handle it.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Power-User

Join Date: May 2006
Location: Bahama, NC. USA.
Posts: 270
Good Answers: 18
#2

Re: Trip Switches on 1ph winch trolley

11/11/2008 2:49 AM

Brock. You haven't supplied a lot of information to work with but if regulations permit I would look into a motor that allows a position sensor to be mounted to the shaft. Then you can have the motor controler programed to stop the trolley at exactly the same place at both ends of the run. You could also add a softstart to allow for a slow smoth start that would reduce the sudden jurking start that you will probly experience otherwise. The use of this type system may fall under different code parameters and eliminate the need for limite switches on both ends. If the system wasn't well thought out in the beginning you may have to discard the current components and start over. Information such as distance? Whinch cable run? Does the same power source supply both ends now? Does the trolley run on rails or is it suspended from the cable? Would all be helpfull.

Wish you success. J.Conway

__________________
For every great advancement in medicine there is an equal and opposite advancement in the denial of treatment.
Register to Reply
Anonymous Poster
#3

Re: Trip Switches on 1ph winch trolley

11/11/2008 5:47 AM
In addition to the comment 1 - caution to take that Limit switch contacts to be of heavy rating / + thru Auxilliary contactor to make motor on / off.

You have to use top positioned limit switch to stop when motor goes in up direction

and limit switch positioned in the bottom shall stop the motor when motor in down ( reverse ) direction.

You require 2 power contactors - one for up movement ( forward )

- second for down ( reverse ) movement.

Top positioned limit switch NC contact shall auto maticaaly stop forward contactor when required.

Bottom positioned limit switch NC contact shall automatically stop the reverse contactor when required.

other electrical interlocks between 2 contactors with Aux. NC contacts may also be added to safe guard against preventing 2 commands to reach simaltenously.

guest

Register to Reply
Power-User

Join Date: May 2006
Location: Bahama, NC. USA.
Posts: 270
Good Answers: 18
#4

Re: Trip Switches on 1ph winch trolley

11/12/2008 2:59 AM

Brock. What's the possibility of a gravity decent with the winch drive disengaged so it will freewheel and a brake on the winch to control decent speed? What type of braking do you have now and how critical is an exactly placed stop?

__________________
For every great advancement in medicine there is an equal and opposite advancement in the denial of treatment.
Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#5

Re: Trip Switches on 1ph winch trolley

11/12/2008 8:33 AM

If I can get the image to post, this is how we did exactly what you have described, but using a 3-phase motor. It should work exactly the same with a single phase motor, assuming the single phase motor is reversible. Not that the contactors require a lock-out device so they can not be activated simultaneously:

Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#6

Re: Trip Switches on 1ph winch trolley

11/12/2008 4:39 PM

I was in the field installing automatic gates for a few years.

This is a very basic circuit and can be found on almost all sliding gate operators.

Google a couple companies and check out their ladder diagrams that they might have on line.

easy peasy

If you're in Chicago? ;)

__________________
High Tolerance is Beautiful
Register to Reply
Power-User
Hobbies - Fishing - New Member

Join Date: Feb 2007
Location: Suva Fiji Islands
Posts: 229
Good Answers: 3
#7

Re: Trip Switches on 1ph winch trolley

11/12/2008 10:51 PM

It is very simple just buy a reversing motor starter from Allen Bradley, Schneider or another supplier this will come with interlocks to prevent the controls from operating together. A couple of limit switches from Schneider or another supplier check out their online catalogues for a suitable design (there are hundreds of them) one will suit you application a few metres of cable and you have a a unit which will comply to all codes and standards.

__________________
"Multa ferunt anni venientes commoda secum, Multa recedente adimiunt". (The years as they come bring many agreeable things with them; As they go they take many away).
Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); coconutpete (1); cwarner7_11 (1); JE in Chicago (1); Jerrell Conway (2); Kilgore Trout (1)

Previous in Forum: Residual Current Circuit Breaker   Next in Forum: how to select overload for 3 phase
You might be interested in: Overhead Trolleys, Tie Down Straps, Industrial Winches

Advertisement