Residual Current Circuit Breaker

11/10/2008 10:16 PM

I am now trying to design a main switch board for my own house; I am having difficulties in choosing a suitable rating for RCCB and the isolator.

The electrical point include

15 nos lighting point.

6 nos 13A 2 gang switch socket outlet

4 nos 15A switch socket outlet.

Assuming that all the electrical points are in use at one instant, the estimated power consumption is 10kW.

The calculated maximum current flow (for 240V, 50Hz system)

=10,000/240

=41.67A

Can I choose an RCCB with current rating 50A or even higher i.e. 100A? How about the sensitivity for the RCCB, 30mA, 100mA or 300mA is more suitable? The current rating for isolator need to be the same as RCCB's or must be higher?

Please advice. Thank you very much...

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#1

Re: Residual Current Circuit Breaker

11/10/2008 10:54 PM

Please Don't.

Unless you are a Qualified Electrician, at which point you should not need to ask these questions. Do NOT try and design and install the Main board or anything else electrical in your home.

Get someone with the appropriate training and skills to do it for you.

Your Familys Lives and your own are worth much more to you than any bill you may recieve.

Playing with what is basically your homes safety system is not worth it.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Reply
Anonymous Poster
#2
In reply to #1

Re: Residual Current Circuit Breaker

11/10/2008 11:19 PM

Thanks for your advice. Definitely I will find a professional person to design it, the question I ask just for my own knowledge. FYI, I am actually a student in Electrical Engineering, I hope I can learn sth from this, hehe...

I hope someone can answer my question. Thanks...

Reply
Anonymous Poster
#7
In reply to #1

Re: Residual Current Circuit Breaker

11/12/2008 8:50 AM

Now there is the best answer yet!

Reply
Anonymous Poster
#3

Re: Residual Current Circuit Breaker

11/11/2008 6:09 AM
dear student,

its good & sensible question that many a practioners do not follow correctly in practice. what you study in text books need to translate in to practice with considerations of lot so many factors like ambient temp. / humidity / non linear electronics load which in herently have leakeges / earthing system available / etc...

for best practices , without going into much details, I can suggest following tricks :

1. RCCB / ISOLATOR current rating > line current * 1.2

2. RCCB leakage trip current rating > inherent leakage current of total+30mA

or > earth resistance of system/50 mA

3. Todays recent developments provide special RCCBs that are free from variations in humidity / electronics loads leakages etc.. then condition 2 shall suffice.

guest

Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#4

Re: Residual Current Circuit Breaker

11/11/2008 4:05 PM

Also please note that the CR4 forum asks you students NOT to try to have the rest of us do your homework for you. How will you ever learn if you cheat?

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply Score 2 for Off Topic
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#5
In reply to #4

Re: Residual Current Circuit Breaker

11/12/2008 12:25 AM

dear student i would suggest collect manufacturer catalogues like ABB,Merlingerin etc go through the same you would find plenty of educational material to select your information the catalogue should be available free or Else log on to the websites of ABB or Merilyn Gerien you would find the information you are looking for.Good luck

CRM

__________________
Run silent run deep
Reply
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#6
In reply to #5

Re: Residual Current Circuit Breaker

11/12/2008 6:19 AM

Its usual practise not to put the lighting circuit on the same RCD as the rest, either no RCD on the lights or a seperate circuit. Reasons - they always seem to trip at night and filament lamps often short to earth when they blow.

Most manufacturers supply boards already split in this way

__________________
A day without a smile is a day lost
Reply
Anonymous Poster
#8

Re: Residual Current Circuit Breaker

11/12/2008 9:00 AM

That is not how to do a load calculation,but I'll assume 41 Amps as max. Use the smallest load center 60 amp service.Split your 15 lighting points inhalf(7 on each circuit) using#14awg copper.Others go onto their own fuse/breaker circuit.This is a easy days work of wiring for one person. Good Luck.

Reply Off Topic (Score 5)
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#17
In reply to #8

Re: Residual Current Circuit Breaker

11/13/2008 2:25 PM

Good advice for North America, but I suspect this guy is elsewhere due to a mention of 220v 50 Hz.

Reply Off Topic (Score 5)
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#18
In reply to #17

Re: Residual Current Circuit Breaker

11/13/2008 5:20 PM

The problem with any sort of code compliant advice is knowing which jurisdiction the questioner is in.

As a designer I face the opposite problem. Quite often I have to ddesign a system to be compliant to a code I am not familiar with or the customer intend to use th eboat in a place wher some products are not available. I recently specified a Bussman circuit breaker only to have the customer declare the local Bussman distributor insisted ther was no such thing. I sent him th eUR of the North American catalog. The Boat was being built to North American spec but builder yard is in Europe. Likewise the customer asked for my opinion of a certain product. Try as I might i could not find the URL, Kept geting a 404 error. Eventually Sparkstation explained that Google has a continental filter and "directs google search based on origin of questioner not on location of URL company.

In common parlance I do not see use of RCBO or RCD in ABYC spec but find it constantly in CE European marine spec. But to then try and explain this to a builder located in mainland china . . oh boy! it gets complicated.

__________________
Elnav
Reply Off Topic (Score 5)
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#19
In reply to #18

Re: Residual Current Circuit Breaker

11/13/2008 7:52 PM

SURE ENOUGH!!

About 25 years ago I was working on a modem for export to Australia. The bloody thing worked perfectly here on the bench, but never there. I never was able to find anything wrong with it.

After Spark's treatise on the Australian power system, I begin to wonder if that might have been the whole problem.

Of course 25 years ago, none of this existed... no CR4... no internet...

Today I think we both know who to ask.

Bill

Reply Off Topic (Score 5)
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#20
In reply to #19

Re: Residual Current Circuit Breaker

11/13/2008 8:05 PM

I ran into the same problem only last spring. the client complained that a certain US built product kept failing within a few months of being installed. After reviewing the product spec and talking to their application engineer I realized what the problem was. Although Europe is nominally a 230V system, the mains peak voltage will on occasion spike beyond 300V. 230V is an RMS rating not the peak.

The product was rated for a max peak voltage of 300V. Apparently the PIV rating of the input circuit could not withstand any more. Poof! There goes another one!

__________________
Elnav
Reply Off Topic (Score 5)
Participant

Join Date: Sep 2008
Location: India
Posts: 3
#9

Re: Residual Current Circuit Breaker

11/12/2008 9:20 AM

Hai friend,

In regard to your requirement, please refer some good catalogues by reputed manufacturers. The following points may be kept in mind.

The current rating must account for the starting surges in your system.

The leakag current rating must be selected in regard to your earthing effectiveness and please do keep in mind that wrong selection of this will cause intermittent tripping whcih in your life would be highly unwanted,

As a thumb rule , please select the current rating as 3 times the total rated current. The isolator current can be 50 mA.

Moreover standard manufacturers have the devices with good combination ratings.

REgards

BINNY

__________________
Binny T R , VSSC , ISRO, Tvm
Reply
Participant

Join Date: Jun 2008
Location: Durban, South Africa
Posts: 3
#10

Re: Residual Current Circuit Breaker

11/12/2008 10:04 AM

Hi there,

If everything is exactly as you described in your request, then it's quite simple:

You can adequately use a 50 A RCCB for that Load together with 50 A isolator. The RCCB sensitivity shoul be 30mA.

Hope you're satisfied.

__________________
Aaron, HVDC technician
Reply
Anonymous Poster
#11

Re: Residual Current Circuit Breaker

11/12/2008 10:04 AM

I do not recommend that you do any electrical design yourself.It is dangerous, as well as illegal in most cases.However, if you would like to see examples of how to calculate loads in various instances, consult the 2008 National Electrical Code HANDBOOK.It is hardback, and has examples and illustrations that are very helpful, whereas the standard NEC codebook does not go into much detail on HOW to do things, it simply states how things should conform to the code.

Good luck in your career.The goal of a school of any kind is to teach a person how to learn, because what you learn today will soon be obsolete, and you must never stop learning in order to succeed.

Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#12
In reply to #11

Re: Residual Current Circuit Breaker

11/12/2008 1:53 PM

My understanding is that NEC = National Electric Code but this is a North American term. Does every country refer to their electric code as NEC? For example Canada and the US both have a NEC book. However these two books differ greatly in some details. In Canada the rules are determined by CSA and in the US by UL. Sometimes CSA and UL agree but other times does not.

Example: I was horrified to learn that in Florida it is apparently acceptable to wire both white neutral and green gorund wires to the same common bus bar. This contravenes the Canadian code which require electrical distribution panels to have the neutral bus bar isolated from the steel enclosure.

In Canadian made power panels the white neutral bus bars are insulated from the metal box, but is joined to the ground bus and box enclosure and thus grounded, by a special brass screw. A cardboard note in fastened to this brass screw reminding the installer to remove the screw if the panel is a sub panel rather than the main service entrance panel. Canadian code prohibits having more than one main grounding point for a residence. The ground point must be at the main service entrance.

Mention is made to RCB in the original post. I realize this is common in 230V 50Hz countries. N. American standards usually require individual outlet protection in the form of a GFCI ( ground fault circuit Interruptors). The trip threshold is set at 5 milliamp for 120V. Do all 50Hz countries use a 30ma threshold for the RCB?

\

__________________
Elnav
Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#13
In reply to #12

Re: Residual Current Circuit Breaker

11/12/2008 3:51 PM

Elnav,

It's not the 50hz, It's the 230V that sets the 30mA, although for certain commercial applications upto 300mA is available to cater for the issues associated with Switch Mode Power Supplies.

In Australia a 40A\30mA RDC is required at the Point of Supply as a Minimum, anything installed on branch circuits are an optional extra.

Regards,
Sapper.

__________________
It's all about the Boom! - MythBusters
Reply
Power-User
Hobbies - Fishing - New Member

Join Date: Feb 2007
Location: Suva Fiji Islands
Posts: 229
Good Answers: 3
#14
In reply to #13

Re: Residual Current Circuit Breaker

11/12/2008 10:36 PM

Re RCDs under yhe new regs 2007 individual rcds are required for each circuit

__________________
"Multa ferunt anni venientes commoda secum, Multa recedente adimiunt". (The years as they come bring many agreeable things with them; As they go they take many away).
Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#15
In reply to #14

Re: Residual Current Circuit Breaker

11/12/2008 10:43 PM

Which Electrical Authority governs Fiji?

__________________
Elnav
Reply
Associate

Join Date: Jul 2008
Posts: 37
#16

Re: Residual Current Circuit Breaker

11/12/2008 10:46 PM

Hi

RCCB is residual current operated circuit breaker with out integral over current protection.

for house hold rather than using RCCB, i advise to use RCBO which is Residual current operated circuit breaker with integral over current protection, the advantage of using this is u need not to pur RCCB and Isolator, RCBO work as RCCB and as isolator too,

only the thing that matter is the Rating of that device, normally any electrical devices are designed to withstand 15 to 20 % more power then its intended rating,

so RCBO of 50A of main current rating and 100 mA of leakage current rating is suitable for your requirements.

Best regards

divyesh patel

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#21

Re: Residual Current Circuit Breaker

04/12/2024 9:26 AM

Choice of <...RCCB...> is based on a number of factors.

  • If the <...house...> is on TN-S or TN-C-S earthing, it probably won't need one. If it is on TT, however, 100mA would be a typical trip setting, selected so that a line-to-earth fault or a neutral-to-earth fault will cause it to trip on imbalance.
  • The disconnect rating depends upon the rating of the feeder cable circuit protection device, which might be a 60A, 80A or 100A fuse (UK), among other things. Clearly, the device needs to survive continuous operation and also disconnection at this level of current.

The question that must arise is why there isn't one already. Or, if there is one, why is it deemed worthy of replacement.

In any case, it is recommended that it be selected, installed, tested and certified as safe by a local qualified Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 21 comments