Hi everyone,
I am working with conveyors. Their drives are 3 phase squirrel cage induction motors. The project people designed in such a way that, the actual load is only half of motor KW by considering the future extension of tph and some other factors. We are mostly having Siemens (DOL) feeders. We are supposed to set O/L setting lesser than the available range in feeders since normal load is only half of the full load current. We accomplished this by inserting O/L relays of required range in feeders or by replacing MPCB.
For example a 30kw motor feeder is having a over load range of 45-63A. But the normal load is only 28A. So the O/L setting should not be more than 34A(28*1.2times) for the protection of equipments.
1.Can we use 22KW feeder for 30kW motor for getting requiired O/L settings? The starting current of 30kw motor is higher than 22kw motor and it is independent of load. Would it make any problem after long use?
2. If we insert one O/L relay having required range in 30kw feeder, Would the starting current of motor affect the relay?
3.Is it agreeable changing the standard design of Feeders?
Kindly give your valuable suggestions,
Thanks in advance.