Blower Motor for Air Conditionner

10/15/2006 8:44 AM

I've a problem of using fan motors in an air condition application:

The motor is three phase, 60 Hz and rated 460 V +/- 10% but facility I've has power supply rated 380 Volts +/- 10%

Please tell me the side effects of using such power supply for short time and long run time on our air con.

Regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#1

Re: Blower Motor for Air Conditionner

10/15/2006 11:48 PM

destruction. Motor will run at 60% of rated power and may well fail to synchronize on start under load = failure is imminent.

Get a three phase autotransformer to step uo the voltage

__________________
Per Ardua Ad Astra
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Blower Motor for Air Conditionner

10/15/2006 11:59 PM

Note that your motor rating is under 60Hz. What's the frequency of your 380V 3-phase power supply? Is it 50Hz, or 60Hz?

You better off buy yourself a correct motor!

OZ

Register to Reply
Participant

Join Date: Oct 2006
Posts: 2
#3

Re: Blower Motor for Air Conditionner

10/16/2006 12:40 AM

Hi Hazkhod,

Please check on the motor terminal connections. There might be a provision for reconnecting the motor wiring to fit your power supply of 380 V.

With your motor terminally connected to the 460-V configuration, it will deliver less torque than normal.

Regards,

Neil

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#4

Re: Blower Motor for Air Conditionner

10/16/2006 6:51 AM

I suspect the 380 volt supply is at 50 Hz. If so it should work OK but power output and speed down to 5/6. Current and torque unchanged.

Assuming the fan is on a friction-only system, power absorbed is down to (5/6)3 = 0.58, so motor is not overloaded. But air flow is down to 5/6 and pressure to (5/6)2. If the fan is part of a complete aircon system needing airflow based on 460 volt, 60 Hz this is unlikely to be enough. If it's been salvaged and fitted to a different system it depends what the requirements are.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: Blower Motor for Air Conditionner

10/16/2006 7:46 PM

Don't forget, speed will be 5/6 as well.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster
#6

Re: Blower Motor for Air Conditionner

10/17/2006 4:37 AM

refer to electrical hand books and find your answer2

Register to Reply
Participant

Join Date: Oct 2006
Posts: 2
#7

Re: Blower Motor for Air Conditionner

10/17/2006 4:57 AM

Hi guys,

3-phase motors with 12 wire-leads out on the terminal are generally designed to work at 220 V, 380 V and 440 V. At 440 -V supply, the motor must be wired using delta connection. At 220-V supply, it must be wired using a double-delta connection. On the other hand, if the supply is 380 V, as in this case, the motor should be wired at double-wye connection. This latter connection produces 380/sqrt(3) = 220 V on every coil of the motor, thereby, drawing the required amperage for steady-state operation.

Please check on the terminal and see the connection. The problem might be solved.

Regards,

Neil