Earth value for PLC as per BS

11/13/2008 2:05 AM

What is the typical earth value as per BS for PLC or DCS system?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#1

Re: Earth value for PLC as per BS

11/13/2008 8:19 AM

Dear all,

There should be no earthing resistance value for PLC or DCS since all earthing must be integrated into one earthing system. If PLC or DCS vendor requests isolated earthing electrode for their systems, it may come from their lack of knowledge. As long as I know, most of the requests for isolated earhting electrodes were withdrawn after some technical clarifications with vendors.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia