VFD Output Voltage

11/13/2008 2:31 AM

Supply voltage/Freq for VFD = 440VAC/60Hz and Output Voltage/Freq is measured at 360VAC/50Hz having a 45kW exhaust fan motor as Load.

Is the output voltage of VFD be affected when frequency is adjusted to a lower value?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: VFD Output Voltage

11/13/2008 7:57 AM

eggslime; usually the voltage rises as the frequency rises up to a limit perry

Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#2

Re: VFD Output Voltage

11/13/2008 8:40 AM

Dear all,

Your are correct, many VFD's are V/f constant. In lower frequency, voltage to be reduced to avoid magnetic saturation in a motor.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: VFD Output Voltage

11/13/2008 1:05 PM

More specifically, when you program a VFD for a particular motor voltage, the VFD sets up and maintains a specific Volts per Hertz ratio. As long as that V/Hz ratio is maintained, the motor will put out full torque. So as the Hz is reduced, so must the voltage be reduced to maintain a constant ratio. So if you had set up your VFD for a 440V 60Hz motor, the V/Hz ratio was 440/60 or 7.33:1. When you turn the frequency down to 50Hz, the voltage becomes 50*7.333 = 367V.

If your VFD is set up for a Variable Torque (Quadratic) load such as a centrifugal pump or fan, the reduction in the V/Hz ratio is no longer linear because the load would require less torque as speed decreases. That might explain why your output voltage is a little less than expected. If that is the case, hopefully you are not using it on a load that requires constant torque, such as a conveyor or machine tool.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (1); Anonymous Poster (1); JRaef (1)