DG Set Basics

11/20/2008 2:41 AM

how to know the current taking capacity of dg set from its kva rating

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#1

Re: DG Set Basics

11/20/2008 11:18 AM

pranayshah; single phase divide kva by voltage will give you amps. for 3 phase divide by 1.73, divide by volts perry

Register to Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#2
In reply to #1

Re: DG Set Basics

11/20/2008 11:25 PM

this is the basics

Kva=V×i×cosΦ

Where v=Volts,i=Corrent in amphs and cosΦ(power factor)=0.8 for generators single phase

For three phase it is √3 V×i×cosΦ (0.8 power factor)for generators

CRM

__________________
Run silent run deep
Register to Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2007
Location: India
Posts: 42
Good Answers: 3
#6
In reply to #2

Re: DG Set Basics

11/21/2008 2:22 AM

Dear CRM,

The formulae given by you for single phase and three phases are for the out put of DG Set in KW and not for out put in KVA

V.Ambarani

__________________
Best Regards
Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2008
Posts: 2
#7
In reply to #6

Re: DG Set Basics

11/21/2008 7:15 AM

what will be for kva base dg set.

if my dg is 25 kva , 3 phase.

Then as per 25000=400* Amp

Amp =62.5

which i think is misleading.

Register to Reply
Associate

Join Date: May 2008
Location: City : Chandigarh, Country : India, Continent : Asia, Planet : Earth, Galaxy : Milky Way, Universe
Posts: 54
Good Answers: 1
#3

Re: DG Set Basics

11/21/2008 1:06 AM

Most DGs are rated at 0.8 power factor. In 415 V, 3 Phase, 50 Hz standard countries like India, the rated per phase DG / Source current is = (KW)/(415*0.8*1.732). For your information, usually the DG vendors insist on loading of DG to maximum 85% of the rated current capacity.

Regards,

Sanjeev

__________________
Karma is Dharma
Register to Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#4
In reply to #3

Re: DG Set Basics

11/21/2008 1:21 AM

as per ISO for declaration of rating and power the engine is designed to operate with a power factor 0.8 engine world wide are manufactured as per ISO if you try to improve power factor to say Unity or 1 your engine will be over loaded and may trip or call for frequent overhauls and replacement of engine earlier then defined by engine manufacturer hence every engine manufacturer publishes in print the rating of the engine at Power factor 0.8

CRM

__________________
Run silent run deep
Register to Reply
Associate

Join Date: May 2008
Location: City : Chandigarh, Country : India, Continent : Asia, Planet : Earth, Galaxy : Milky Way, Universe
Posts: 54
Good Answers: 1
#5
In reply to #4

Re: DG Set Basics

11/21/2008 1:25 AM

power factor improvement above 0.8 should not be a problem as long as the total active power rating of the load falls within the rated active power rating of the DG.

rgds

Sanjeev

__________________
Karma is Dharma
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

chhotu1990 (2); crm (2); perry (1); pranavshah (1); V.Ambarani. (1)

Previous in Forum: Standard Specs for Soft or Annealed Copper Wire   Next in Forum: Dry Type transformer

Advertisement