The manufacture of the mezzanine should be able to answer your question. They should be able to make recommendation size and type. The manufacture of the anchor will be able to give you instructions as to how to apply it.
__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
A standard A307 bolt with standard hex head will develope it's full strength when embedded 10diameters into the concrete (3000psi concrete). It must be at least 4diameters from the nearest vertical edge. This is for pull out strength only. For lateral loads, it takes a seperate analysis. For example. a 1 inch A307 bolt can safely withstand a pull-out force of it's area times 20000 pounds (safe allowable stress),i.e., .785 square inches x 20000pounds per square inch allowable equals 15700 pounds, when embedded 10 inches into 3000psi concrete.
Most engineering offices that must size anchor bolts have tables that have allowable loads for various size bolts.