We are going to convert our 16MVA(33/6.6kV,50Hz) Transformer to 20MVA(33/6.6kv,50Hz) Trasnformer by Converting cooling system from ONAN(Oil Natural Air Natural) to ONAF(Oil Natural Oil Force).
For this change we need to replace our existing CTs at 6.6kv side from 1500/1 to 2000/1 for Metering/Over current E/f protection/Differential protection/Restricted E/f Protection.
Specification of Existing two core CTs for Metering & Xmer Differential
CT No.1
| 1500/1-15VA,CL 0.5,CORE 2 CTR-1500/1-10VA CL-PS,VK>300V,Imag<30mA AT VK/2,DIFFERENTIAL PROTECTION WITH RELAY DTH31(ALSTOM MAKE),
RCT<=4.75OHM,RATED:7.2KV,25KA,1SEC,BIL:75KV PEAK |
Specification of Existing two core CTs for Overcurrent-E/f & Restricted E/f Protection
CT No.2
| SINGLE PHASE TYPE,CORE 1 CTR-1500/1-15VA,CL 5P10,CORE 2 CTR-1500/1, CL-PS,VK>150V,Imag<7.5mA AT VK/2,RESTRICTED E/F PROTECTION WITH RELAY FAC14(ALSTOM MAKE),
RCT<3.6OHM,RATED:7.2KV,25KA,1SEC,BIL:75KV PEAK |
Here Manufacturer can able to give these CTs with RCT value at 75 deg <= 8 Ohm(against 4.75 Ohm) and at 75 deg <= 6.5 Ohm(against 3.6 ohm) for CT no. 1 and 2 with confirming all other specification.
Can I goahead with this deviation in RCT Value and I would also like to know the impact of this deviation in technical point of view.
thanks
SJ