Steam Turbine Tripping

12/02/2008 4:33 AM

we have one 15 MW steam Turbine which was tripping on under frequency in steady state without any addition of load. This phenomenon was repeating frequntly giving no clues. The tripping is at random and sudden and no chance for saving the turbine from tripping. The following checks were carried out both by O & M Team and OEM.

1) AVR was checked found OK

2) Electronic Governor checked no problem noticed

3) Generator Protection Relay (Beckwith Make) checked tripping the set on actual low frequency parameter.

4) Mechanical side checking like governing oil filter, nitrogen pressure of accumalator

etc were done but no clues for tripping.

5) At lat I /H Converter was changed

but unfortunately testing of 5th point could not be done as generator tripped on rotor earth fault, during this period turbine was also opened and found that 7 nos of Curtis wheel blades were missing, after repair work of both turbine and generator machine was put back on service. after restarting we are not experiancing any under frequency tripping.

now the question is whether the problem was with I/H converter or Curtis missing blades is not clear, can any one think and revert.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Mechanical

12/02/2008 4:55 AM

Hello rangacharya

<"....during this period turbine was also opened and found that 7 nos of Curtis wheel blades were missing, after repair work of both turbine and generator machine was put back on service. after restarting we are not experiancing any under frequency tripping.....">

  1. Were the Curtis Wheel blades all in a cluster together or near each other on the turbine wheel? (Out of balance problem)
  2. Where did the missing blades end up?
  3. Advise RPM of turbine rotor shaft.
  4. Advise diameter of damaged wheel.
  5. Was the alternator rotor insulation resistance tested before attempting repairs?
  6. If answer to (5) above is "Yes", then advise the actual measured resistance please.
  7. If an alternator is tripping out, it is normal to test all protection relays plus insulation resistance of rotor and stator coils, also sliprings etc. as a matter of course - Such Insulation testing to be applied for at least 15 minutes per coil, to allow for capacitance to ground and other coils.
  8. Advise alternator output voltage please.
  9. Advise rotor coil voltage max. please.
  10. How old is the machine?
  11. Was the input steam too wet, and that caused the blade damage?
  12. Does the installation have other same make/size units installed, if so have these been checked for similar blade cracks or damage?
  13. Other useful information, advise please.

Reply here and you may be assisted.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru

Join Date: Jul 2008
Location: Anywhere I may be at the time
Posts: 661
Good Answers: 16
#2

Re: Steam Turbine Tripping

12/03/2008 1:25 PM

Why not install the original convertor and the question would be answered?