pole slipping

12/02/2008 10:40 PM

What are the reasons for pole slipping in an alternator in a power plant?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Anonymous Poster
#1

Re: pole slipping

12/02/2008 11:23 PM

Pole slipping typically occurs under severe fault conditions which cause a transient torque on the generator which exceeds the ability of the field to hold the generator rotor synchronised to the stator. A generator is most susceptible to this problem when it has a low excitation, as this produces a weak magnetic field. For this reason, capability diagrams show the stability limit for the machine when in an under-excited state. Outside of this line, pole slipping becomes a real possibility in the event of a system fault.

The 'slip' occurs when the rotor experiences a sudden physical and electrical shift in position relative to the stator, after which the field recovers enough strength to lock the rotor back in synch with the stator. When his occurs, the violent acceleration and deceleration associated with pole slip causes enormous stress on the generator and prime mover, and may result in anything from winding movement to shaft fracture or worse. It is a very serious fault.

Register to Reply Good Answer (Score 2)
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#3
In reply to #1

Re: pole slipping

12/04/2008 11:14 AM

GA! You need to register for this place.

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Power-User

Join Date: Oct 2008
Location: Meherrin Virginia
Posts: 319
Good Answers: 6
#2

Re: pole slipping

12/04/2008 7:32 AM

If your unit has a loose tie with the system the problem is more likely to occur. Some OEM's provide a protective system called Early Valve Actuation that on sensing a fault fast closes selected valves to reduce power input in hopes of preventing the situation.

__________________
If you fail to follow through, you will fail.
Register to Reply
Associate
United States - Member - Member Engineering Fields - Power Engineering - New Member

Join Date: Jun 2007
Location: Texas
Posts: 52
#4

Re: pole slipping

12/04/2008 12:48 PM

Also look at low excitation.

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jconn_ETEC_05 (1); otha (1); Turbotroll3 (1)

Previous in Forum: Dual Display   Next in Forum: ferroresonance

Advertisement