Generator Residual Protection relay

12/07/2008 12:22 PM

Hi, I have a situation where a power generator is used to supply 400v 3 phase to a distribution board. This DB has 6 single phase loads ( Airconditioner) and 2 electric motors 3 phase each. How do I install an earth fault relay to protect the generator. The generator has 3 phase and a neutral point conection. Am just wondering if I use a residual current relay, the relay may trip if I switch on either of the electric motors since the electric motors do not have a neutral connection. Please advice.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#1

Re: Generator Residual Protection relay

12/08/2008 7:24 AM

Is this an emergency generator or a stand alone power system? And why 400v?

If it is an emergency generator. Your gerenrator should be grounded with as a separately derived system, but it should also be attached to the source source ground throught your transfer switch.

If it is a stand alone power source then it should be grounded as such, and all equipment attached should be grounded per code and engineering standards.

I have never had to put a fault relay on such a small piece of equipment.

Register to Reply
Associate

Join Date: Sep 2008
Posts: 31
#2
In reply to #1

Re: Generator Residual Protection relay

12/09/2008 1:55 PM

Hi, it's an emergency generator,400v phase to phase, 560KVA. The neutral point was connected to the power switchboard but isolated from the plant earth. The generator was grounded from its equiptment earth bud ( i.e body of generator ).

So I was wondering if I put a residual earth fault relay on the 4 core cable( 3 phase and 1 neutral) that ran from the generator to the switchboard, would it work?