Service Grounding / Bonding

12/11/2008 2:52 AM

If both ends of a 4" GRC pipe is "bonded" with 4/0 stranded copper and a fault occurs with a 1600 amp main? Is it really better to bond both ends of the pipe or just one end? I understand the NEC to say only one end or the other of the pipe needs bonded. Is there an adverse reaction if both sides are bonded, with the Grounded conductor continues through the pipe. Yea Yea Yea artical 250. 66 Im looking for theory. and I just got Punked by an Inspector. That one HURT!!!!!! If it matters "4 Full boats" 500kcm Feeders

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Dec 2008
Location: Kuwait
Posts: 27
#1

Re: Service Grounding / Bonding

12/12/2008 1:31 AM

Two thoughts on reading through your message come to mind. Are you considering the grounded conductor size in relation to the largest "ungrounded" conductor?

Next: The GRC threaded connections are not always 100% conductive and may break the bonding requirements of the installation. Ungrounded conductors shall be

no smaller than 12.5 percent the size of the largest ungrounded conductor!

Hope the RE-inspection goes well...

__________________
Mark Abell
Register to Reply
Associate

Join Date: Dec 2008
Location: Kuwait
Posts: 27
#3
In reply to #1

Re: Service Grounding / Bonding

12/12/2008 8:13 AM

Slight typo on my earlier response. The sentence explaining that the "Ungrounded conductors shall be no smaller than 12.5 percent the size of the largest Ungrounded conductor! The first word of this sentence is clearly a typo. THE CORRECT SPELLING SHOULD BE "Grounded". (Probably not worth writing about but I don't want to mislead)

__________________
Mark Abell
Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#2

Re: Service Grounding / Bonding

12/12/2008 7:52 AM

If I am reading this right, the GRC is simply being used as protection for a grounding conductor. If this is true there is no reason to bond the GRC at both ends. The bond is being used to prevent the GRC from "choking" the amperage if there is a fault.

Bonding at both ends doesn't make it any better or any worse, other than the GRC becomes part of the grounding conductor.

As far as the inspector goes he is the "Jurisdiction having authority" making him, by law, correct. It is a problem I have struggled with for forty years. My advice, play nice, if it doesn't cause a possible fire or shock hazard, then its just a difference of opinion.

Register to Reply
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#4

Re: Service Grounding / Bonding

12/12/2008 9:05 AM

When you say "pipe" I assume that you actually mean the electrical conduit from the meter base to the panel...

If you bond both ends of a grounding conductor that is bonded to a transformer neutral (i.e. ground to neutral in meter-base and ground to neutral in distribution panel) then you effectively parallel the grounding conductor (in this case your conduit) with the nuetral conductor. Thus your ground will carry 1/2 of the electrical current that is supposed to return through the nuetral conductor and the pipe could shock people when they touch it if the resistance is low enough. Generally this does not happen because the pipe is an easier path to ground than the person touching it.

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 17
#5

Re: Service Grounding / Bonding

01/06/2009 7:43 PM

both ends of the conduit protecting the grounding conductor are bonded to prevent lightning induced current from "choking off" the ground current path.

it's in the book