Siemens Relay - Transient Dimensioning Factor

12/12/2008 4:13 AM

As we all know that CT transient overdimensioning factor is given as (1+X/R) , for 120 MVA relay value is about 21(20+1) but siemens have given transient overdimensioning (kt) as 4 for transformer differential protection, Pls somebody explain this in details.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#1

Re: Siemens Relay - Transient Dimensioning Factor

12/24/2008 12:24 AM

What's 120MVA relay?

__________________
BNDas
Register to Reply
Member

Join Date: Dec 2008
Location: chennai
Posts: 9
#2
In reply to #1

Re: Siemens Relay - Transient Dimensioning Factor

12/30/2008 1:33 AM

SORRY this is 120MVA transformer

Register to Reply
Participant

Join Date: Jul 2011
Posts: 3
#3

Re: Siemens Relay - Transient Dimensioning Factor

08/23/2011 3:43 PM

Yes, siemens is giving value 4/5, there is different equation for other relay makes, as a basic equation Vknee=2 Ifs (Rct + 2 Rloop), what is basis of this equation to any standard?,

Register to Reply