Strange phenomenon at a power transformer

12/20/2008 6:24 PM

Dear All,

We have a strange phenomenon at one of our transformers.

One 33/11kV oil filled transformer, at the time it is energized through 33kV SF6 gas circuit breaker, we observe a flash at the flanges which connect the tank and top plate.

The flash does not continue, only at the instance when the transformer is energized.

We have two transformers with the same specifications, but only one of them has the flash, and this occurs every time it is energized.

Does anybody know what is this phenomenon?

Best Regards

Akihito Shigeno

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Strange phenomenon at a power transformer

12/21/2008 7:16 PM

Oh I don't like the sound of that, it sounds like a flash-over of some sort during transformer inrush at switch on. Where does the flash occur - on the circuit breaker or the transformer?

You really should find out for sure what is going on before running this system as your equipment may be damaged (faulty manufacturing, transport damage, damaged winding or bushing, etc) and could fail prematurely or when the transformer output load is connected.

Can you supply more information including posting a picture indicating the location of the flash, and the transformer VA rating.

__________________
jack of all trades
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#2
In reply to #1

Re: Strange phenomenon at a power transformer

12/21/2008 9:16 PM

Dear All,

There is a flash at the transformer every time at the moment it is energized.

We checked transformer bushings, and found no damages.

The flash runs between flanges of the top over and the transformer tank.

There is a gasket between both flanges, so the top over and the tank are not directly touched.

There are around 60 sets of bolt and nut to tighten the flanges. These bolts and nuts are of stainless steel and insulated from top or tank flanges. The Insulation is done with insulation sleeves and washers. Transformer vendor says, the insulation for the bolts are to avoid corrosion between steel flanges and stainless steel bolts.

The top over and the tank is bonded with two bonding wires at two locations.

Does anybody know the reason of this phenomenon?

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3
In reply to #2

Re: Strange phenomenon at a power transformer

12/21/2008 9:56 PM

Based on what you are saying it sounds like the top and bottom of the transformer tank are completely insulated from each other (like the two plates of a capacitor) and you are getting a flash-over.

First, are you sure the bonding wires form a low resistance path between the top and bottom of the tank? No corroded metal or broken wires breaking the circuit?

__________________
jack of all trades
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#4
In reply to #3

Re: Strange phenomenon at a power transformer

12/21/2008 10:55 PM

Dear all,

Yes, top and tank are insulated except for two bonding jumpers.

We measured the resistance, with a multimeter, between top and tank, and result is nearly zero Ohms.

To remove the insulation from the bolts may be a solution, and we are preparing to do so. However, we would like to know what is cause of the flash over between flanges.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Anonymous Poster
#5
In reply to #2

Re: Strange phenomenon at a power transformer

12/22/2008 12:00 AM

I would suspect the bonding attachments

Clean all mating points of the bonding system, including retapping the bolt holes.

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#6

Re: Strange phenomenon at a power transformer

12/22/2008 12:11 AM

It is a possibility that the bonding is not sufficient to conduct all of the charging current. After all you replaced the connections of quite a few bolts with only 2 conductors while creating a large capacitor.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 23
#7

Re: Strange phenomenon at a power transformer

12/22/2008 12:36 AM

Please check the transformer body earthing. Is it connected properly? If connected properly please check the earth resistance.

As another measure please enrgise the transformer from 11kv side keeping the 33 kv breaker OFF. Observe any spark at the flange.

Secondly the 33kv insulator may apparently look Ok but may be there a small creapage which might be giving way at the time of energisation due to inrush of current during switching.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#8

Re: Strange phenomenon at a power transformer

12/22/2008 2:58 AM

You have said both the transformers are identical.Have u removed the insulation of the bolts in the transformers where there is no flash?if not removing may not be a solution.What u say as flash is an arcing and needs more detailed investigation and I think the manufacturer should be involved .

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#9

Re: Strange phenomenon at a power transformer

12/22/2008 4:59 AM

Dear all,

Thank you everybody.

Both transformers are identical, they are with insulated bolts for top and tank flanges. We have not removed the insulating material from the bolts. Transformer manufacturer has agreed to supply replacement bolts and we will replace the bolts with new ones but without insulation.

After the bolt replacement, top and tank flanges will be electrically connected at many points where uninsulated bolts are installed. Induced current in top and tank can freely circulate without producing voltages, we guess, there will be no more flash.

However, we still have a question. Where or how the voltage, which causes a flash, is induced between top and body flanges at the moment the transformer is energized.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#10
In reply to #9

Re: Strange phenomenon at a power transformer

12/22/2008 6:02 AM

Reply to Akihito Shigeno

Could it be contact bounce when you close the breaker?

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#11
In reply to #9

Re: Strange phenomenon at a power transformer

12/22/2008 5:14 PM

I'm grasping at straws here but I have an idea not mentioned by anyone else here. The brief higher than normal inrush current that charges the transformer primary might make the transformer housing act as an additional transformer secondary wiring itself. The chassis could then produce sufficiently high voltages across the bolt insulation to cause a spark. Try different phase wirings as an experiment.

Best of all for the group would be a posted picture of the arc site.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Anonymous Poster
#12

Re: Strange phenomenon at a power transformer

12/22/2008 8:05 PM

did you do pf test on hi side, to top, and hi to tank? in addition to all xfmr tests prior to commisioning the unit? what are results?

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#13

Re: Strange phenomenon at a power transformer

01/03/2009 11:13 PM

Hello Akihito,

Few questions,

a) What is the vector group of the transformer? is it Dyn11?

b) If it is Dyn11 , has the neutral of the low side grounded?

c) Is the body of the transformer bonded to a good earth?

d) I would recommend isolating the transformer and conducting insulation test on HV/lv windings.

cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#14
In reply to #13

Re: Strange phenomenon at a power transformer

01/05/2009 4:31 AM

Thank you all,

a) What is the vector group of the transformer? is it Dyn11? Yes, Dyn11.

b) If it is Dyn11 , has the neutral of the low side grounded? Yes, LV side neutral is grounded.

c) Is the body of the transformer bonded to a good earth? Yes, Transformer tank is grounded to the grounding network.

d) I would recommend isolating the transformer and conducting insulation test on HV/lv windings.

Hi-potential test for both HV and LV side was conducted before power cables are permanently connected.

I will report you the result after energizing the transformer without insulation at bolts.

Best Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Associate

Join Date: Feb 2009
Posts: 34
Good Answers: 4
#15
In reply to #14

Re: Strange phenomenon at a power transformer

02/17/2009 5:30 PM

I have been watching this discussion & have extra questions

Can you provide details of the differences in the transformer circuits.

Are there surge arrestors on one transformer but not the other, are there different circuit breakers?

What is the length of line feeding each transformer & from the CB to the transformer.

Are the two transformers at the same site or are they in different locations?

Are you energising on-load or no-load?

The results of the bolt changes will be good to understand but if it corrects the problem - then you have to question if the other unit will develop the same problem over time.

__________________
Murphy was an optimist....
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#16

Re: Strange phenomenon at a power transformer

04/05/2009 9:41 PM

Dear all,

This is the final report for this subject.

We replaced insulation at the bolts and nuts with washes called "contact washers".

With the contact washers, transformer body and top flanges are bonded at many places (more than 50) around the flange. There is no more flash after that.

I still have the original question, where the voltage which caused the flash came from. Anyway, thank you very much.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Register to Reply 16 comments
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (5); Anonymous Poster (2); chaterpilar (1); CJMcGill (1); horace40 (1); jack of all trades (2); KRW43 (1); nesubra (1); redfred (1); SABNAVEES (1)

Previous in Forum: Carbon brushes & sliprings   Next in Forum: Formula for optimalization Condenser Steam turbin
You might be interested in: Transformers, Power Transformers, Telecom Transformers

Advertisement