Inrush Current in Transformers

01/07/2009 8:29 AM

hi to all,

please explain how can calculate the inrush current in transformers???

appreciate you co-operation.

thanks,

eng. sanad,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Inrush Current in Transformers

01/07/2009 8:27 PM

Google your question. There were a number of hits including these:

http://www.ametherm.com/Inrush_Current/transformer_case_study.htm

http://www.bambangdjaja.com/index.php?option=com_content&task=view&id=22&Itemid=34

ASk the manufacturer of the transformer what the inrush is. It is 10 to 12 times the full load amps.

Register to Reply
Associate
United States - Member - Member Engineering Fields - Power Engineering - New Member

Join Date: Jun 2007
Location: Texas
Posts: 52
#2
In reply to #1

Re: Inrush Current in Transformers

01/08/2009 9:06 AM

I would agree that inrush is usually measured, not calculated. The manufacture data sheet for small equipment, or factory acceptance test for larger equipment should specify a range of inrush. For 1 to 2 MVA transformers at ~5%Z, I've used eight to ten times the overload rating with out trouble.

If you are trying to setup up protective coordination, you should be calculating the bolted fault current and arc fault current (IEEE 1584 or IEC equiv), use the lower of the two as a high limit. Then use the estimate of inrush as a low limit, for your instanteous action settings.