Kindly describe the method or calculation for calculating the value of Resistance in NGR with respect to the rating of transformer/Generator and also respect to the voltage.
Binod Kumar Panda
Engineering Fields - Power Engineering - Siswanto
Good Answers: 15
Re: What is the formulla for calculating the resistance value of a NGR.
01/09/2009 2:51 AM
Dear pandebinod.....
pls click the following address...
http://www.postglover.com/Literature/HR003-05_High_Resistance_Ground_Gde.pdf
www.benderrelay.com/datasheets_US/Mining book _FULL PAGES_6c.pdf
http://www.startco.ca/library/papers/PowerTestPaper.pdf
Goodluck
Rgds
Sis
LOVE FORUM AND DISCUSSION
01/09/2009 4:04 AM
33kv substation
Re: Calculating Resistance Values
01/09/2009 8:52 AM
What's an NGR?
01/10/2009 2:51 PM
NGR = Neutral Grounding Resistor = Device used to limit current to ground in the event of a short to ground.
Always use protection.
01/09/2009 12:31 PM
Pandabinod,
From the definition of power; S [VA] = U [V] * I [A] and U [V] = I [A] * Z [Ohm] => Z[Ohm] =(U^2)/S, where S = apparent power, U = voltage, I = current, Z = impedance, R = resistance; [..] being the respective units of measurement.
If only active (real) power is involved, Z = R and so R = U^2/S.
Scientes et audaces fortuna juvat !
01/10/2009 3:00 PM
I am not sure what that formula is all about but what you have to determine is what amount of current can be safely shunted to ground that will allow all of your safety breakers to trip if they are upstream of the short but not damage any transformers or motors that are in the circuit. R=E/I, whereas E (voltage) is a given, I (current) is your perceived limit according to your equipment ratings, and R (resistance rating) is to be solved for. I am sure that if you want help you can contact the manufacturer of a commercial NGR for much better help than you have received here.
Try this one: http://www.avtron.com/neutral_grounding_resistors.htm