Instruments for Impulse Lines

01/09/2009 9:38 AM

hello everyone

we have hot crude service where we have clogging of impulse line frequently .we generally fill up with glycerine . I want to know what are the standards for the impulse lines and the manifold require for the installation of transmitter ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Instruments for Impulse Lines

01/13/2009 12:10 AM

The reason for clogging can be due to surrounding cold atmosphere. The Transmitter for liquide service should be hooked up below the process line, as this is the basic principle of Hook up. Moreover if the liquide is hot crude oil, it should not clog. You can flush the impulse fully and can reconnect it.

Register to Reply
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#2
In reply to #1

Re: Instruments for Impulse Lines

01/13/2009 11:24 AM

High temperature and pressure seems to be unsafe for flushing , this is the reason that I want to know the standard of the impulse line so that one can work safely . also if crude is hot should not be clogged, this is why I want to keep the Impulse line as near as possible .But I can't work out without standards can u help me out from this problem

regards

find2am

Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#3

Re: Instruments for Impulse Lines

01/14/2009 2:01 AM

Hi there,

The manifold should be double isolation and equalisation. This means you can isolate both the high pressure and low pressure impulse line. The valve in the middle will equalise the pressure between the high pressure and low pressure side of the transmitter.

Depending on the pressure and process - you might want to use a purge type of measurement. Failing this - you will need to get a safe filling medium that has a higher density/sg than the crude - this will ensure that the crude never gets into the impulse lines.

Regards,

Craig

Register to Reply
Anonymous Poster
#4

Re: Instruments for Impulse Lines

10/08/2010 11:25 AM

On your transmitter what happened if you forgot to isolate your equalizer and open both low pressure side(LP) and high pressure (HP)

Register to Reply Off Topic (Score 5)
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#5
In reply to #4

Re: Instruments for Impulse Lines

10/11/2010 12:27 AM

Nothing would happen to the transmitter - you would not damage it if thats what you mean.

Because the equaliser is open - your HP and DP side of the transmitter should be at equal pressure - thereby giving you a zero reading (well as close to zero as possible).

Regards,

Craig

Register to Reply Off Topic (Score 5)