Earth Electrodes

10/27/2006 8:29 AM

What is the max impedance value aloud when used with a 100mA rcd time delayed trip on a domestic instalation

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: earth electrodes

10/27/2006 2:57 PM

Max touch voltage allowed is 50V

so 50V/100ma = 500 Ohms

Max earth electrode resistance is 500 Ohms.

Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: Earth Electrodes

10/28/2006 7:36 AM

I'd be very unhappy with an earth impedance greater than a few ohms, RCD or not. I strongly suggest you take advice from a local qualified electrician.