Squirrel cage amperage related question

01/12/2009 9:10 PM

I work on industrial air compressors. One I worked on the other day had a blown fuse on the 230VAC single phase circuit that powers two squirrel cage cooling blower fans on the frequency drive for the machine. I found that the inlet air filters for the frequency drive section were completely clogged and were preventing air flow through the frequency drive. Now, that being said and the fuse being replaced and both fan motors running and checking out just fine, would the blown fuse been attributed to: 1- clogged filters causing too hot an environment for the fans and thus amp draws increasing past nominal, or 2- loss of air flow due to logged filters and that being what put stress on the motors themselves and amps increasing then fuse blows. I have a customer that seems to think on a squirrel cage type blower, if you block off inlet air completely, the amperage decreases. I thought it was the complete opposite. I'm basically looking for some kind of trusted site i can print off some kind of theory to make my case. Thanks for your time!!

Travis Wilson.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: Etherville
Posts: 12362
Good Answers: 115
#1

Re: Squirrel cage amperage related question

01/13/2009 2:49 AM

I have a customer that seems to think on a squirrel cage type blower, if you block off inlet air completely, the amperage decreases. I thought it was the complete opposite

I don't know the answer, but tell him to move before he gets burned or falls off.

__________________
For sale - Signature space. Apply on self addressed postcard..
Register to Reply Off Topic (Score 5)
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#2

Re: Squirrel cage amperage related question

01/13/2009 7:51 AM

" if you block off inlet air completely, the amperage decreases. I thought it was the complete opposite"

When you block the inlet of any blower, it is no longer doing any work. So the amperage will decrease. The more air it moves, the harder it's working. Less air, less work, less current.

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: Etherville
Posts: 12362
Good Answers: 115
#3
In reply to #2

Re: Squirrel cage amperage related question

01/13/2009 12:34 PM

no longer doing any work

I don't get it - If the intake is blocked, isn't the impeller still turning and effectively trying to create a vacuum ? ie, it's load increases and it would burn out ? I'd like some further explanation/re-assurance before I test this on something. From your description, it sounds like I can duct-tape the inlet to Mrs K's hair-dryer, set it to cold, and all will be OK ?

__________________
For sale - Signature space. Apply on self addressed postcard..
Register to Reply
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#4
In reply to #3

Re: Squirrel cage amperage related question

01/13/2009 1:44 PM

It's true! However, no longer doing any work is an overstatement though. You are still doing some work.

I've actually proved this. I had a manager make the statement that a dirty filter will cause a motor to draw excessive current. I said no. So, I had to prove it, with a 60hp blower. I cut a piece of plywood the same size as the filter. I them put on a clamp meter. We took a reading with no filter, then with the plywood in place of the filter. The current went way down with the plywood in place.

It's somewhat counter-intuitive, but when you think about it, you need a lot more power to move a large volume of air, than not.

But don't try it with the wife's hairdryer. The airflow in that unit also provides cooling for the motor. That's not the case with an industrial blower. The motor has it's own impeller to do that.

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: Etherville
Posts: 12362
Good Answers: 115
#5
In reply to #4

Re: Squirrel cage amperage related question

01/14/2009 2:08 AM

Ah, it becomes clearer. Thank you Bricktop. Damn shame I got impatient to test the hairdryer.

__________________
For sale - Signature space. Apply on self addressed postcard..
Register to Reply
Power-User

Join Date: May 2008
Location: Europe
Posts: 285
Good Answers: 9
#6
In reply to #4

Re: Squirrel cage amperage related question

01/14/2009 3:22 AM

Bricktop G.A.

Is the same principle true for a water pump ?

Regards

Mr. W.A Snow

Register to Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#9
In reply to #6

Re: Squirrel cage amperage related question

01/14/2009 5:32 AM

For a centrifugal pump ,yes, normally. It will damage the pump though, through cavitation (Kris' vacuum doing some destructive work). Flow reduction is best done on the discharge side via a valve. Is it an efficient method, no. That is why VSD devices are built.

Having said all that and fully agreeing with Bricktop, some pumps and fans behave in an odd manner. Just a small percentage, but they are beasts.

To the OP to satisfy yourself and anyone else with an interest, use Bricktop's test method (your digital multimeter will record the current if you don't have a tong that is accurate at low current) and let us all know how you went.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #3

Re: Squirrel cage amperage related question

01/14/2009 5:29 AM

Yup!

You will also hear the speed of the motor INCREASE as the load is reduced (no more air passing though!!)

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#18
In reply to #3

Re: Squirrel cage amperage related question

01/15/2009 10:12 AM

Just a supplement to Bricktop's explanation: if you stop the airflow, air doesn't move into and out of the region swept be the fan blades - so the fan isn't accelerating anything much. That means the fan blades are freeer to rotate. If DC powered (or AC powered and slipping), the motor can accelerate and generate a larger back-EMF; if it's AC driven and not slipping, the phase of the back EMF will advance and the effect will be similar.
Sorry if I've used the terms loosely.

N.B. I thought I might find you in this custom-built cage - but I'd hoped you might obey the law and refrain from smoking indoors.

Register to Reply
Guru

Join Date: Mar 2007
Location: Etherville
Posts: 12362
Good Answers: 115
#20
In reply to #18

Re: Squirrel cage amperage related question

01/15/2009 1:40 PM

Thanks Andy & Fyz (and Bricktop fro the original), i'll get back in me cage.

The funny thing is, I can smoke in my own house, but if I ask any sort of worker in.......... Mark my words, it's the thin end of a wedge. < rant restrained>. If you have a piano, start making plans for when you have to surrender more than just the keys to your house. It will all be burnt upon the bonfire of the politically correct vanities. We'll have the freedom of choice, but from a select list.<oops, I slipped>

__________________
For sale - Signature space. Apply on self addressed postcard..
Register to Reply Off Topic (Score 5)
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#21
In reply to #20

Re: Squirrel cage amperage related question

01/15/2009 4:30 PM

Smoke in your own house? Ridiculous!
Even if it's detached and your neighbours don't sue for recklessly putting their homes at risk, don't the social services provide any sort of protection for kids round your way (probably best not answer that bit)?

Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Location: Etherville
Posts: 12362
Good Answers: 115
#22
In reply to #21

Re: Squirrel cage amperage related question

01/15/2009 7:40 PM

If I don't keep up the Kipper supply Del will savage me ! My supplies from Inverawe aren't enough to share with him, and procrasternating didn't help. Hoodies don't smoke as good as Oak, but it's pleased the neighbours no end.

__________________
For sale - Signature space. Apply on self addressed postcard..
Register to Reply Off Topic (Score 5)
Power-User
Engineering Fields - Electrical Engineering - Not so new Member Popular Science - Weaponology - New Member Hobbies - Fishing - New Member, old hobby.

Join Date: Nov 2008
Location: Windhoek, Namibia, South west africa
Posts: 410
Good Answers: 23
#7

Re: Squirrel cage amperage related question

01/14/2009 5:26 AM

Good day Compressit,

some motors have thermo cut-off fuses which are ampere rated & thermally rated.

I think that a clogged filter would increase the internal drive temperature & thus would cause the fuse to do its job. Drives contain senitive electronic components that are sensitive to things such as power surges, cooling & mechanical shock. Most drives have certain ventilation sepcifications that have to be adhered to when installing.

I hope this clears matters a bit.

kind regards

__________________
tHe days of good inglisH haz wented.
Register to Reply
Power-User

Join Date: Nov 2008
Posts: 158
Good Answers: 1
#10

Re: Squirrel cage amperage related question

01/14/2009 5:57 AM

I like the accurate answers I see. Furthermore, overheating due to blocked filters can contribute to a blown fuse by preventing flow through (if applicable) and certainly body cooling of the motor(s). Check the amperage while running under full load as well as the voltage and compare it to the nameplate. Also check start amps & duration. There's always a reason a fuse opens. Is this direct drive?

Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#11

Re: Squirrel cage amperage related question

01/14/2009 7:32 AM

Very good boys and girls, we have all discovered that as a conductor heats up resistance increases causing less current to flow. However, we have failed to answer the original question by Compressit.

Why did the fuse blow (overcurrent protection) or has Compressit mistaken a thermal protection device as a fuse?

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Not so new Member Popular Science - Weaponology - New Member Hobbies - Fishing - New Member, old hobby.

Join Date: Nov 2008
Location: Windhoek, Namibia, South west africa
Posts: 410
Good Answers: 23
#12
In reply to #11

Re: Squirrel cage amperage related question

01/14/2009 7:51 AM

I dunno uncle goat.

I are not the sharpest tool in the shed so I wait to see what compressit says.

__________________
tHe days of good inglisH haz wented.
Register to Reply
Power-User

Join Date: Nov 2008
Posts: 158
Good Answers: 1
#16
In reply to #11

Re: Squirrel cage amperage related question

01/14/2009 5:43 PM

Right on GROG. You're up to your usual 100 years of experience! (compliment intended)

How many "technicians" just replace the fuse?

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#19
In reply to #11

Re: Squirrel cage amperage related question

01/15/2009 10:28 AM

Once more into the fray of chaotic diatribe with some cited information. From the Littlefuse designer's guide of 1988. "The current carrying capacity tests of fuses are performed at 25 °C and will be affected by changes in ambient temperature. The higher the ambient temperature, the hotter the fuse will operate, and the shorter its life will be."

Enough said.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#23
In reply to #11

Re: Squirrel cage amperage related question

01/16/2009 10:49 AM

The conductors heating is a secondary effect, which will take some time to occur. Cutting off the airflow has an immediate effect - far faster than the heating. This is best illustrated by covering the inlet to a vacuum cleaner hose.

As Andy said, when you block off the airflow, the motor immediately runs faster (indicating it is doing LESS work pumping air). With many vacuum cleaners, the same airflow that does the cleaning also cools the motor, so if the airflow is blocked very long, the motor will overheat and either shut itself off or burn out.

Unless the fuse is located in the air stream the heating should not blow the fuse, because less current is flowing, not more.

Now if the VFD has a sensor that tries to regulate air flow, it may have tried to increase current to keep the same flow under restricted conditions. That could definitely blow a fuse.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#13

Re: Squirrel cage amperage related question

01/14/2009 10:24 AM

AHHHHHHHHHHH! No no no no. How many of you remember about phase angle involving reactive loads? How many of you even have the faintest idea what I'm talking about? The real power drawn by the motor is P=VIcos(Θ). The magnitude of the current drawn by the motor does drop in a non-linear fashion as the slip speed approaches zero. The slip speed is the difference between the synchronous rotational speed and the rotor speed. But until one externally drives the motor shaft to convert the motor to a generator, the internal losses are not compensated to cause a significant drop in current. So the motor is still producing mechanical work.

Now that I've gotten that tantrum over with, the lack of air movement did cause the motor and fuse to overheat. All fuses have a temperature degradation of their holding current rating. This overheating may have increased the drag slightly by dimensional changes of the bearings and thus once again slightly increased the drawn current closer to full current draw. Possibly the motor overheating started some mild breakdown of the winding insulation and caused a sharp increase of current drawn but when this happens it is usually is a permanent failure.

My conclusions come from studying the textbook, "Electric Machinery Fundamentals" by Stephen J. Chapman published by McGraw-Hill. While their maybe a web site that does publish this kind of information, I do not know of a web site that does. Since a little bit of knowledge is dangerous, some things are best learned in a classroom.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#15
In reply to #13

Re: Squirrel cage amperage related question

01/14/2009 5:06 PM

Good answer, both from and Tomad but you were first and backed it up with documentation. If I were teacher I would give you an A.

I know this is simple minded but you do deserve some praise from someone.

Register to Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#14

Re: Squirrel cage amperage related question

01/14/2009 12:39 PM

Compressit,

The current drawn by a squirrel cage motors (induction motors) practically does not change if the total output power remains the same, irrespective if it is ventilated via a fan or not. But the balance between the heat developed in a motor (due to losses in windings, mechanical losses, etc) and the heat dissipated via its fan is distorted in case fan air input is blocked, so the created heat leads to an increase in the temperature of the motor and ultimately may lead to damaging the electrical insulation, etc.

If the motor is driving a fan, the output power of the motor has to match the required power input of the fan. This power is dependent on the fan characteristics (power (HP) versus air flux (cfm). When gradually blocking the air input of the fan, the power required increases up to a point and, for a total input block, it decreases.

So, with air input totally clogged, the power drawn by the driving motor is less than the rated output power (less current drawn). So basically your customer was right.

__________________
Scientes et audaces fortuna juvat !
Register to Reply
Participant

Join Date: Jan 2009
Posts: 2
#17

Re: Squirrel cage amperage related question

01/14/2009 6:48 PM

Thanks to Tomad and redfred and all others for their input. To clear up any confusion, yes it was an overcurrent protection fuse (8 amp to be exact) that blew not a thermal protection device (unless there is something called a thermal protection device that looks like a fuse and says time delay and 8 amps...). I do feel slightly dumb for thinking lack of airflow would increase motor amp draw even though in my head this seems like a logical explanation. Anyway, the motors show fine now when tested with a multimeter. Amp draw, voltage balance and windings all check out fine. I'm just going to have to assume that the heat of the frequency drive was what took it out. I really dont see any other way to look at it. Oh, yes one more thing. The contacts of the motor starters also chout out fine. Once again thanks so much for all the replys even though this question seemed kind of sophomoric.

Travis

Register to Reply
Register to Reply 23 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Bricktop (2); Compressit (1); dkwarner (1); DRFREON (2); Emjay4119 (1); GRAY HAIRED OLD GOAT (2); HoleInTheSnow (1); Kris (5); Leonf (2); Physicist? (2); redfred (2); tomad (1)

Previous in Forum: coefficient of friction   Next in Forum: open source CFD

Advertisement