Restarting a Delta Motor After One Winding Opens

01/21/2009 10:31 AM

There is an overhead door at work that will start to open but then stops. I don't know all the details because I haven't been out to the door yet, but the information has been given to me by one of my guys.

The door is driven by a 3-phase 480 volt motor. I don't know anymore information than that. I don't know the hp or if its delta or wye connected or anything else, I have not seen it. The guys tell me they don't see anything mechanically wrong with the door, and that it operates smoothly by the manual chain.

I am told that the C-phase thermal overload element was found completely fried. I found this to be unusual being that the overload relay's purpose is to open up the control circuit to protect the motor, in this case the heater couldn't even protect itself! This is a bi-metal type OL set at 115%. So aside from assuming the OL relay took too long to trip, they did the following checks:

They took Meggar readings phase to ground from the load terminals and the insulation for all phases was acceptable. They did a continuity check phase to phase and said there was continuity.

The workers proceeded to replace JUST the C-phase thermal element with a new one.(without replacing the entire O/L relay) They started the motor and the same thing happened, the motor started, the door started to open and then stopped, it tripped on thermal OL, but yet again the C-phase O/L heater was fried.

They took resistance readings again this time from the motor with the line connections determed. They paid particular attention to the exact ohm readings this time and got 20,20,40. The electric brake was determed as well, and was not a factor into these readings. One of the guys explains the readings by saying it is a delta motor with one winding burnt open. I asked him if he could read the nameplate, but he could not.

I understand that a single-phased motor will continue to run once started due to inertia and the one phase being energized, BUT I though it could NOT re-start. His theory was that an "opened" delta could re-start if it had all three-phases supplied to it, it would still energize 2 out of 3 phases, energizing enough poles to give it the necessary magnetic fields.

Can anyone explain some theory behind single-phasing, and if it is possible to restart a delta-wound motor that has had one winding burnt open?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#1

Re: Can delta motor re-start after one winding opens?

01/21/2009 11:20 AM

The delta motor should even start - with one winding is open. I don't know why it shuold not re start in this condition

The rotation of the EM Field will still be there - with a jump - so the currents in the phases (remaining) may be un-equal and this may create the problem of over-loading of individual phases.

One similar article I could get by a quick search, (no use of quoting my old rusted book , and any way i have to search the relevant chapters on motor faults ) I hope this will be enough.

http://www.progress-energy.com/custservice/carcig/resourcectr/presentations/MotorProtection_VoltageUnbalance.pdf

Refer the page 4 of this article.

"The motor will continue to drive the load till it burns out or properly sized relays take it off line"

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#2

Re: Can delta motor re-start after one winding opens?

01/21/2009 2:11 PM

Sorry-- didn't mean to post here.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Anonymous Poster
#3

Re: Restarting a Delta Motor After One Winding Opens

01/21/2009 10:33 PM

You say it starts then fails shortly...then cooks the overoad...windings etc.... all okay...High resitance across contacts on the contactor or relay when energized will do this...or a low voltage leg on the 3 phase...Should not even start on two phases...will "growl" and single phase with no movement..an overload is a fancy fuse...you can still cook them......In my experience , if a motor moves and then gives me an issue...it drops a phase , has increased amps due to a poor connection , or mechanicals bind causing resistance and increased load causing the problem...

Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Restarting a Delta Motor After One Winding Opens

01/22/2009 2:11 PM

ok I understand a motor won't start when one phase of voltage being supplied from the source is lost due to a blown fuse, a bad contact or even a destroyed overload heater. The motor will only have a single phase combination of voltage availabe and has no phase differential to start spinning.

What I want to understand is:

*if all 3 phases of the supply voltage are balanced and available to the motor

AND

*the motor is a Delta with one winding open, will the 3-phase voltages going through the two good motor winding phases be sufficient to create the phase differential and starting torque to get the rotor spinning?

Despite the fact the currents will increase and trip the overload device and bad things in general would happen, I just want to know if this theoretically possible.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#5

Re: Restarting a Delta Motor After One Winding Opens

01/22/2009 10:23 PM

Please refer to my post #1 and the referred link

Do you want to repeat the same explanations ?

There are only 4 posts can you not go through them before asking a question ?

Also if a single phase is out don't you think two more are still available ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Anonymous Poster
#6
In reply to #5

Re: Restarting a Delta Motor After One Winding Opens

01/23/2009 9:09 AM

sb,

Yes, thank you I did read your post and the attached link. The link only discusses single-phasing when one phase of supply voltage is lost due to blown fuse, etc, it doesn't go over the theory of a MOTOR winding open with all 3 phase voltages available.

I'm sorry I didn't completely understand your first post, your sentence structure was a little strange:

"The delta motor should even start - with one winding is open. I don't know why it shuold not re start in this condition"

I wasn't originally sure what you were trying to say and wanted some other opinions as well. Anyway thank you for responding.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Restarting a Delta Motor After One Winding Opens

01/23/2009 1:05 PM

Sorry, but sb has misinterpreted. IF THE MOTOR IS ALREADY RUNNING, it will continue to run with an open phase, but it will not re-start with only 2 of the 3 phases. The current and therefore the magnetic fields have no rotation element to it. Others have said this, I am just trying to counter the misinterpretation.

So back to your problem; there are a couple of possibilities I can think of off the top of my head:

  1. The problem is two fold; you have something that is causing an overload in Phase C, AND your trip mechanism inside of the OL relay is welded, so the motor starter never drops out and the overload condition eventually melts the heater element. It is, after all, a "heater" element!
  2. You have a bad / loose connection between the contactor and the overload on Phase C. The added heat from the high resistance of that connection is burning up your heater element. But since the current THROUGH the heater element is not necessarily high, it is not getting down into the relay operating mechanism to cause it to to disengage and trip.
  3. You HAD a loose connection on the heater element itself, then when they replaced it, the connection points on the OL relay are now so badly damaged that you can no longer get a good solid connection when you mount the heater element.
  4. Your motor has a bad connection, but it only shows up when it heats up. So when your guys test it, the circuit looks good, but when the motor runs under load, it heats up and causes an overload. This is a likely co-factor in #1 above.

I would start by first getting rid of that overload relay and replace it with a Solid State version. No chance of resistance / welding problems with those. A good one will also be able to pick up a phase current imbalance, which can be useful in determining the orginal root cause of the fault.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Participant

Join Date: Jan 2009
Posts: 2
#8
In reply to #7

Re: Restarting a Delta Motor After One Winding Opens

01/23/2009 2:59 PM

JRaef,

Thank you for your reply. However the thermal O/L relay DID open and trip the contactor, just not before the heater burnt up. Either way the O/L apparently did not trip soon enough.

To me it's like which came first, the chicken or the egg? Did a bad motor cause the excessive currents which burnt up the overload heater? OR did the heater burning open and the O/L not tripping soon enough CAUSE the motor to be damaged? I don't know what the intial problem was. My recommendation was to change out the motor being that it had bad ohm readings, and replace the entire O/L relay not just the heater. (Unfortunately a solid state device is not feasable for us for the relatively low importance of this overhead door drive motor) We will see if the problem will be solved when those get changed out.

ALSO, to get back to electrical theory, JRaef are you stating that this motor could not restart on 2 phases?

SB seems to support the theory that a Delta could conceivably restart with all the line voltages present but with one motor winding opened up. That was my original question.

This is what someone else told me:

"A three-phase motor will not start with one line open. If the motor is running when single phasing occurs it will continue to run as long as the shaft load is less than about 80 percent rated load and the remaining single-phase voltage is normal (rotation of the rotor produces a quadrature field that maintains rotation). However, excessive vibration and rapid increase in the phase current will damage the motor if it is allowed to continue to run.

If you have an open winding on a delta-connected motor, the motor may be started since you still have a phase difference between the two remaining windings. This of course depends on the load. Note that the line is not open but the winding is. Since the three phases are available and assuming coil A is opened, phases A to C will energize coil C at some phase angle, and phase B to C will energize coil B at a different phase angle (120 degrees apart).

However, a wye-connected motor won't start with an open line or open winding."

Does this seem possible?

Thanks for your replies.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#9
In reply to #8

Re: Restarting a Delta Motor After One Winding Opens

01/24/2009 1:19 AM

If you think on other side the Y may start and not delta

Let us say the phases are

R = V,00

B = V,1200

Y = V,2400

The motor does not know it, and hence the voltage across RB is (say Y has opened)

= (v,00) - (V,1200) and this applies between two phases in series, without any phase shift and thus no rotating field, no toqrue at all.

But you do get it in Y connection , with neutral

Hope i am correct (brushing up what i learnt ages back)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches