Electrical Requirements for an Industrial Park

01/21/2009 12:59 PM
I have a to design a 1000 arc industrial park. The dimension of each plot and and area has been given. We designed the street lights using a HPS 250W with mounting height of 10m and space betwn of 35m.we need design da distribtion to da industries and and provide supply 4 STP and WTP. Also planin on givin 240V supply 2 da street lights. I knw how 2 calculate the voltage drop...but how do u choose the circular mil and K value? also wen calculatin VD for street lamp do u take each lamp and calculate VD or the furtherest 1 frm source. also how do u calculate the current carrying capacity of Aluminium.?how do u select number of feeders?also can u can we get site where we can download NEC 2008.
You want to be notified of new comments but you did not register or login.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Electrical Requirements for an Industrial Park

01/21/2009 9:37 PM

You need to hire a consultant.

Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#2

Re: Electrical Requirements for an Industrial Park

01/22/2009 1:40 AM

If this is homework get your institution or library to get it for you.

If this is for a contract - Not even Zimbabwe would allow it.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Hobbies - CNC - New Member

Join Date: Aug 2006
Location: Western Australia
Posts: 767
Good Answers: 58
#3

Re: Electrical Requirements for an Industrial Park

01/22/2009 2:01 AM

Could you please write the next question in English?

__________________
If you can't explain it simply, you don't understand it well enough. (A.E.)
Register to Reply
Anonymous Poster
#4

Re: Electrical Requirements for an Industrial Park

01/22/2009 8:37 AM

No offense to anyone, but people are paid a lot of money to answer this question.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5

Re: Electrical Requirements for an Industrial Park

01/22/2009 10:13 AM

Lets just answer all sorts of gobbledy gook answers. This way when it blows up, he'll get sued instead of us. Better yet we'll over design the safety margins so that he goes broke. Install everything with nothing less than 1500 kcmil silver conductors. Everything buried under ground in rigid stainless conduit.

Eschew obfuscation.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#10
In reply to #5

Re: Electrical Requirements for an Industrial Park

01/22/2009 10:17 PM

Why not Gold ? (it has a better conductivity)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#11
In reply to #10

Re: Electrical Requirements for an Industrial Park

01/23/2009 8:01 AM

Gold ?So that later some thief can get better remuneration for his hard work .

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#12
In reply to #11

Re: Electrical Requirements for an Industrial Park

01/23/2009 8:56 AM

With all assumption that a 23 year kid is designing a total electrical circuit for an Industrial park and that too a quite large one (hopefully not his project work) We have to keep all the factor of safety in picture.

So assuming that needs a couple of MVA load - let us put in a 200MVA transformer with switched capacitor bank for pf correction.

As mentioned in prev post - the cables (assuming underground) should be SS sheathed (wo do not know the location) with say 2 gauge (comes out to be about 7mm diameter wires) that must be protection if some body wants to trample over it.

These cables can be additionaly routed using schedule 120 pipes (comes out to be about 0.56" wall thickness at 6" or 0.44" in 4")

So the trucks now can not flatten it.

With this amount of protection it may be difficult to replace the cables, so we should go for best conductor- let us go for Ag with lowest resistivity - thus it will have less chances of getting burnt in the pipe or Au since before it gets burnt or the electrical system is messed up due to the design, it will be replaced (because of getting stolen)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Off Topic (Score 5)
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#17
In reply to #12

Re: Electrical Requirements for an Industrial Park

01/24/2009 8:23 AM

Hi sb,

You are absolutely right . Such a large electrical project is to be designed by qualified ,experienced and licenced electrical person and is not a child's play. My comment was only a joke and ment nothing serious.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#19
In reply to #17

Re: Electrical Requirements for an Industrial Park

01/24/2009 8:28 AM

Don't worry, my answer was so too.

Too many students want their project completed at net or project identified at net but why at CR4 ?

You open a link and you don't know the problem is a real one or a paper one.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#13
In reply to #10

Re: Electrical Requirements for an Industrial Park

01/23/2009 9:03 AM

Actually Silver has the highest conductivity of any room temperature metal at 63.01 *10^6 S/m. Gold's conductivity sits at 45.2 *10^6 S/m. Copper sits between these two at 59.6 S/m. Gold has the unique characteristic of not readily oxidizing and high conductivity, this makes it ideal for connector and contact plating.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#16
In reply to #13

Re: Electrical Requirements for an Industrial Park

01/24/2009 8:11 AM

Hi redfred,

Thanks for the details of conductivity of gold , silver and copper. Long time back during sixties we used gold wire as heat fuses for furnaces to protect them from damage by switching off the main control contactor(in case if the temperature control system fails). Considering the present prohibitive cost of gold, now silver is commercially used for contact unless it is very special requirement.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#18
In reply to #16

Re: Electrical Requirements for an Industrial Park

01/24/2009 8:25 AM

The advantage of gold is that it is noble. Ag or Cu will oxidise.

Any way this chart is quite informative

http://hyperphysics.phy-astr.gsu.edu/hbase/tables/elecon.html#c1

only it is for pure metals and we do not usually use pure.

and its home page is a beauty just have a look

http://hyperphysics.phy-astr.gsu.edu/hbase/hframe.html

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6

Re: Electrical Requirements for an Industrial Park

01/22/2009 4:17 PM

You need to hire an engineer with power distribution experience.

Register to Reply
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#7

Re: Electrical Requirements for an Industrial Park

01/22/2009 5:51 PM

Your first sentence answers your own questions. You mean ares (hopefully not acres), so your park is 100,000 m2. This is a huge risk; so you need an appropriate professional with experience, resources and PI insurance coverage. I do this for a living. My professional advice is: get a professional.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#8

Re: Electrical Requirements for an Industrial Park

01/22/2009 5:53 PM

duplicate

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#9

Re: Electrical Requirements for an Industrial Park

01/22/2009 9:58 PM

Hi,

For designing such a large project you need knowledge,expertise, experience,and beyond all conversant with the safety rules ,administrative regulations of the country /state where you want to design the project. As all others stated you need a certified ,competent consultant who has the licence and authority to carry out such a job. while your consultants put forward some technical query which you cannot understand or want a second opinion you are always welcomed to this site. There are many experts here who are willing to help you.

Our best wishes are with you for completing your job . Best of luck for your project .

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#14
In reply to #9

Re: Electrical Requirements for an Industrial Park

01/23/2009 9:13 AM

Bravo, V.I.Abraham.

For legal reasons this man needs a licensed consultant. Along the way this consultant may produce cryptic queries that we can help translate here. You get a GA from me.

My earlier answer was a bit snarky. While it was a great relief for me to vent about something that day, it was not called for. I apologize to all.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#15
In reply to #14

Re: Electrical Requirements for an Industrial Park

01/24/2009 7:44 AM

Hi Redfred,

Thanks friend. the boy might be a student who may be wanting to make a project report or a sample design for a project or something in connection with his studies . He does not know the seriousness of designing such al large electrical work. We all have frightened him so much, that he appears to be scared to react to the replies. Let us hope he will react at least once.

Register to Reply
Active Contributor

Join Date: Jan 2009
Posts: 15
#20

Re: Electrical Requirements for an Industrial Park

01/24/2009 2:39 PM

after reading all your comments I'm surely reluctant to ask. I am electrical eng student whose doing my final year project. This is actually my project I am doing at a company..Its a live project which they have given to us. We are thrown out into the ocean with no guidance. That is why i asked this doubts. Can you please tell me when calculating voltage drop for the cables. the formula used is VD=mV/A/m * Ib*L/1000.

the mV/A/m value is taken from a table.where can i get this value?Where can I obtain this table?

Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#21
In reply to #20

Re: Electrical Requirements for an Industrial Park

01/24/2009 5:01 PM

Your origioal post said "We designed the street lights using a HPS 250W with mounting height of 10m and space betwn of 35m.we need design da distribtion to da industries and and provide supply 4 STP and WTP. Also planin on givin 240V supply 2 da street lights. I knw how 2 calculate the voltage drop...but how do u choose the circular mil and K value? also wen calculatin VD for street lamp do u take each lamp and calculate VD or the furtherest 1 frm source. also how do u calculate the current carrying capacity of Aluminium.?how do u select number of feeders?also can u can we get site where we can download NEC 2008."

1. Where are your located?

2. You can not download the 2008 NEC. You have to buy it.

Voltage drop = amps x resistance of the conductor. Resistance usually is based on a 1000 ft basis. So you will need to calculate R for each span. Remember use conductor distance.

Example: assume that the amperage for 1 light is A and you have 4 poles with lights on one street lighting circuit. The amperage thru the 1st span is 4A, 3A thru the 2nd span, 2A thru the 3rd span and 1A thru the last span. Using the formula the VD thru the first span is 4A x R, 3AxR for the second span etc. To get the total VD add the individual voltage drops together and you have the VD at the last light.

Likely you will be using #4 triplex cable or something similar. Check the following site for cable information. It gives the characteristics for different size cables. You can locate other sites for street lighting.

Register to Reply Off Topic (Score 5)
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#22
In reply to #20

Re: Electrical Requirements for an Industrial Park

01/25/2009 9:59 AM

Hi Roger,

Good that you have reacted at least now. My assumption is correct. You need not be reluctant to ask your doubts. You should have made this statement in the beginning itself.

No body become an expert after passing out of engineering college. It takes years of experience to carry out design work of a project. It is good that you are thrown out with out guidance. Now you have to do your own research . It is hard job which you have to do it yourself so that you learn.

To start with I shall give you some guidance .

1. Make a drawing of the area locating the power source location of the light points with dimension, cable route , method of cable laying ( under ground / overhead) and the electricity rules and regulation of the electricity supplier/ board/ government /municipal authority have to be considered.The budgetary sanction of the project.

2 . Calculate the total load and its distribution ,available power supply( 3 phase/ single phase , voltage) weather conditions and ambient temperature of location

3. Cable size , voltage drop and length calculation will depend on 1 & 2

4. If the cable distribution is under ground the terminal looping and connector boxes have to be designed accordingly. The individual cable from the connector box to the light point will be different.

5. Earthing provision and protective system has to be designed

5. Estimate of materials required and labour cost.

6. Finally estimate the time required for completing the project with available resources

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jan 2009
Posts: 15
#23
In reply to #22

Re: Electrical Requirements for an Industrial Park

01/25/2009 12:35 PM

Thank You Sir for your assistance.it does help with a bit of direction. Sorry for my ignorance.Everything we are doing according to IS norms. We have at the moment designed the scheme of street lights with what distance we will place the street lights and what type of fittings have been chosen. Next we have to calculate the voltage drop to see what conductor size we are using. We using aluminium conductors since it is cheaper for cabling. We are doing underground cabling for providing 3 phase supply to the street lights. We are ignoring the weather conditions and taking in to account the rest. I just want to know the mV/A/m drop for a 4 core Al cable.it is obtained from a table value. Where can i obtain this table?aslo when calculatating the size we have to take into account the short circuit current. is it alrite multiplying the rated current by the factor 3?

Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#24
In reply to #23

Re: Electrical Requirements for an Industrial Park

01/25/2009 7:02 PM
Register to Reply Off Topic (Score 5)
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#26
In reply to #23

Re: Electrical Requirements for an Industrial Park

01/26/2009 6:54 AM

Hi Roger,

Since you are following IS code it is much easy. For Aluminium conductor heavy duty 1.1 kV rating PVC insulated armoured and un armored cables please refer IS 1554 Part I and Part Part II- 1964 ( Rating as per IS 3961 part II 1967). You can design your cable system based on that, it is authentic no body can challenge it. Similar charts with voltage drop is provided by the reputed Indian cable manufacturers also.Their charts are also based on IS .

The ratings are based on following assumptions

a) Maximum conductor temperature 70 ° C

b) Ambient temperature 40 ° C

c) Ground temperature 30°C

d) Thermal resistivity of soil 150°C cm/watts

e) Depth of laying 750 mm

f) Thermal resistivity of PVC 650° C cm/watt

Further rating factor is given for variation of ambient temperature, variation of ground temperature, thermal resistivity etc. for a.b,c,d , e and f

Normally accepted standard and followed (Estimated) Voltage drop for PVC cable 1.1 kV Aluminium conductor is given below.

Sq mm Voltage Drop V/KM/ A

1.5 41.60

2.5 25.00

4.0 15.70

6.0 10.40

10 .0 6.20

16.0 4.00

25 .0 2.50

35.0 1.80

50..0 1.30

The maximum permissible voltage drop is 3%

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#27
In reply to #20

Re: Electrical Requirements for an Industrial Park

01/26/2009 9:31 AM

The National Electrical Code (NEC) has a very boring seminar class to meet the National Fire Protection Association 70 code. It only took me 16 hours (two full work days) to able to interpret the enormous amount of information in this code. This code incorporates many critical characteristics not normally considered by an electrical engineer, and certainly not an engineering student. For an example, what type of insulation material should be used on the conductor, neoprene rubber, teflon, PVC? Does the cable have to be run inside a conduit and what type of material for the conduit? And for a final example, how many power handling conductors will safely fit in a conduit. (Remember these wires will get hot as the draw increases, so filling the conduit with copper will surely eventually cause a fire.) So for an informative exercise continue with your calculations, but you don't have an engineering or electrician's license or insurance to cover yourself. Be careful. As far as your project analysis if you assume that a copper alloy will retain 95% of the conductivity of pure copper, then using the value you have for cable lengths you can calculate the wire resistance. But without knowing the size of your theoretical power distribution grid, you should remember that this may become a transmission line problem.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#25

Re: Electrical Requirements for an Industrial Park

01/25/2009 8:31 PM

It would be a sorry result indeed if your experience of this forum left you feeling like an engineering pariah. Let us see if we can redress this affront.

A free programme which may be of assistance is available here http://www.generalcable.co.nz/NewZealand/NZDownloads/Gencalc.aspx

You will note this is metric and based on NZ conditions. That said, it is worthwhile exploring all avenues of information especially as a student. You may never know where you may end up, what regs you may need cognisance of, why certain regs are more applicable than others and what factors influence an answer.

For volt drop of site lighting:

(a) you need to position your site distribution points (DPs) which are sometimes referred to as street lighting pillars (SLPs). From these each circuit of street lighting emanates. Each SLP contains the circuit breakers / fuses and the contactor for control. The contactor is normally connected to a photocell atop the nearest column; control wiring is required therefore to this column.

(b) use the full load current of all fittings on all circuits (don't forget including ballasts) and apply to the length of the feeder cable to the SLP, to calc VD to the SLP. We assume the SLP is fed directly from the main board. If not, VD to the sub-board must also be considered.

(c) apply the full load current of a circuit to the length to the first column + the average of the rest of the circuit (i.e. distance from first column to last ÷ 2). This will give the max volt drop in the circuit. Normally, you do this only for the longest circuit. Add VD to (b).

(d) Calculate the volt drop in each column. This is the load of a fitting (& ballast) over the length of the column cables (in your case 10 metres). Add VD to (c) for the max volt drop to the fitting.

(e) Don't necessarily hang your hat on aluminium. Cu gives lower volt drop and therefore smaller cables; bear in mind you have to get the cables into and out of the base of each fitting. The cut-out in the column base will only be capable of cables of a maximum size.

(f) consider the geometry; it may be possible to form a ring circuit to reduce volt drop.

(g) depending on local regs, it may be necessary to use an RCD. Consider therefore the leakage current of the ballasts, especially electronic versions.

Best of luck.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply
Register to Reply 27 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); BabyGuinness (2); Hendrik (1); redfred (4); Roger30121985 (2); sb (4); The Prof (1); V.I.Abraham (7); wareagle (5)