REF Protection

01/22/2009 7:12 AM

why will a REF protection not operate for a thourough faul that is the fault outside the protected zone as even in that case current unbalance will b there ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: REF Protection

01/23/2009 5:39 AM

dear sir,

Ref protection is an unit protection, which operates only for the internal faults. For external faults the differential protection will sense and operates before the REF prot. So REF doesn't operate for the external faults.

Am I correct?

Regards,

Kailash

Register to Reply
Member

Join Date: Jan 2009
Posts: 9
#2
In reply to #1

Re: REF Protection

01/23/2009 5:54 AM

i don't agree sir.

what if there is only REF & no differential protection?

Register to Reply
Anonymous Poster
#3

Re: REF Protection

01/24/2009 3:08 AM

Hi

REF means Restricated Earth Fault

it is a zone protection or unit protection which operates when fault has taken place in particular zone or in unit,

for outside fault, there will be a current imbalance but this imbalance current will also return back throuh neutal of the zone, so current in the zone remains balanced even if fault has taken place outside the zone,

Best regards

Divyesh patel

Register to Reply