Sustaion Earthing resistance

01/23/2009 3:17 AM

Dear sir

1) what is minimum Earth resistance need to maitain for indivisual

Plate eathing or Pipe Earthing in substation

2) We are using 66kv/11KV, 25/35MVA, Star/Delta transformer but we are using solid Earthing(Plate) on star(HV) side, but know our customer asking indivisual Eartpit resistance shall be with in one ohm.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Nov 2008
Location: Bangalore
Posts: 22
#1

Re: Sustaion Earthing resistance

01/23/2009 12:37 PM

For 66/11KV sub station, yes, earth resistance shall be maintained (practically) within 2 ohm. If you are able to achiev within ONE ohm is very good. You can achiev this by following methods

  • Use CI pipe earthing or
  • Connect more no of GI / Copper earth pits( Plate or pipe earthing) in series or
  • Crerate more earth mats with 50x10 sqmm Copper flat
  • By chemical earthing if your natural earth resistance is more
  • Use bentonite clay to increase the erth resistance by increasing water retntion
  • Mainly check tightness and increase the area of contact
__________________
Let Noble Thoughts Comes to Us From All The Sides
Reply
Power-User

Join Date: Aug 2007
Location: N.E. Alberta 55.6329 N Lat. 111.0729 W Long. Canada
Posts: 216
Good Answers: 7
#2

Re: Sustaion Earthing resistance

01/24/2009 5:12 AM

Most substations, I have built, had to be < 1 ohm. As the other fellow said, series of grd rods or a deep well, we used a deep well with a series of grd rods. Its not so much as the star connection, but the fault current and the lightning protection.

__________________
Could be worse, it could be me. :)
Reply
Commentator

Join Date: Aug 2011
Posts: 76
#4
In reply to #2

Re: Sustaion Earthing resistance

08/24/2011 1:58 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Reply Off Topic (Score 5)
Member

Join Date: Oct 2008
Location: UK
Posts: 8
#3

Re: Sustaion Earthing resistance

01/24/2009 5:38 AM

The old criterion used to be <1ohm to combine HV/LV earths....but the KEY issue is the magnitude of the 'fault current' that the earth system will need to handle safely.

Newer regulations are steering away from the 1 ohm rule and more towards using modelling software such as CDEGS to 'prove' the safety of your design/install by modelling the EPR (earth potn rise).

Go to http://www.sestech.com/ for details of the s.ware and/or www.ees-group.co.uk for more info.

Reply
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

electricaleng (1); mayt2u (1); user-deleted-1092 (1); vinukumar (1)

Previous in Forum: Can I Use a Washing Machine Motor as an Alternator?   Next in Forum: Meggar Test

Advertisement