Dear all,

In the last two years, 2 times blast accured in siemens LT busbar.One 132 Kw motor feeder is there. Last year,While starting the motor blast occured near the incoming laira of the feeder. Suspected the laira tension.

So the supply to motor diverted to another feeder(nearer to the burnt feeder). Last week, same type of blast occured again at the time of running nearer the diverted feeder. No foreign materials observed. the busbar is capable of withstanding the starting current of motor. The reason for blast still not found.

Could anyone help me to find out the reason?

Thank you

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Blast in Siemens LT busbar

01/26/2009 4:20 PM

What does "laira" mean?

This is all I could find...

http://en.wikipedia.org/wiki/Laira_(comics)

Generally, when a "blast" occurs in bus bar systems, it is related to a short circuit event.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Anonymous Poster
#3
In reply to #1

Re: Blast in Siemens LT busbar

01/27/2009 8:47 PM

Laira means (female) power connector. The system is 415V system. No moisture & dust.Still flashover happened.

Reply
Active Contributor

Join Date: Oct 2006
Posts: 17
Good Answers: 1
#2

Re: Blast in Siemens LT busbar

01/27/2009 5:40 AM

Yes, what is laira means?

This I could offer, probably you have an insulation breakdown? during the high surge of current, a pin hole in the the insulation is enough condition for the breakdown. Loseness, carbonized contact or connection and dust would also contribute to your problem.

You haven't said all the parameters of your problem. (voltages) Anyway,

Check also ambient humidity and temperature requirements for your system. Enough moisture in the air will also ruin your system.

What is your application?, Is soft starting can be done? so that current surge will be dramatically controlled? or Variable Frequency Drive applicable?

Question?

Does your voltages drift down significantly during starting? Have you check its transient response time? Just asking...

Hope this help.

Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#4

Re: Blast in Siemens LT busbar

01/30/2009 5:44 AM

Hi there,

You need to check your busbars for the correct torque. You must have no loose connections etc. I also suggest you get someone out who will check your MCC bus bars for you with an injection set. This will tell you if there is a problem with the insulation, shorting, hot spots, resistance etc etc.

Good luck

Craig

Reply
Commentator

Join Date: Jan 2009
Posts: 62
Good Answers: 4
#5

Re: Blast in Siemens LT busbar

01/31/2009 5:45 PM

Your problem seems to be in the insulation. Check individually the bus insulators if they are leaking.

__________________
Patriotism is the last refuge of scoundrels
Reply
Reply to Forum Thread 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); craigza (1); JRaef (1); juliangelique (1); myn1996 (1)

Previous in Forum: Neutral Grounding Contactor in Diesel Generator   Next in Forum: 200-hp DC Motor - Field Winding Connections

Advertisement