Previous in Forum: Method Statements for Oil-Filled Transformers   Next in Forum: Connecting a Generator in Parallel
Close
Close
Close
3 comments
Rate Comments: Nested
Active Contributor
Technical Fields - Technical Writing - New Member

Join Date: Mar 2007
Location: Port Sudan
Posts: 16

Lead Alloy Sheaths for Power Cables

01/29/2009 6:05 AM

Hi

I need your help if it possible for explaining the purpose of the lead alloy sheath of power cable and if you have any reference or stander to be refer for

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#1

Re: Lead Alloy Sheaths for Power Cables

01/29/2009 10:08 AM

It depends on the type of power cable. Are you referring to low pressure, oil-filled underground power cable?

Register to Reply
Active Contributor
Technical Fields - Technical Writing - New Member

Join Date: Mar 2007
Location: Port Sudan
Posts: 16
#2
In reply to #1

Re: Lead Alloy Sheaths for Power Cables

02/01/2009 4:14 AM

Yes

low pressure, oil-filled underground power cable

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#3
In reply to #2

Re: Lead Alloy Sheaths for Power Cables

02/02/2009 9:59 AM

The lead sheath contains the oil, which provides electrical insulation. In this type of cable, the insulating medium is oil soaked into a paper wrapping. Each conductor is wrapped in paper to ensure separation from other conductors and the grounded lead sheath. When the oil is pumped into the cable, it soaks into the paper, providing a consistent insulation cross-section. The lead prevents the oil from leaking out. If the paper dries out, the loss of insulation will cause cable failure by short circuit.

Medium voltage cables should have a pressurized oil tank at one or more locations along the cable route. A line from the tank is soldered into the lead sheath to provide extra oil to make up for minor leaks. Monitoring the level in the tank provides early warning of a leak, which can then be located and repaired before the cable fails.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

Bluestone (1); Khalid A/Rahim (1); pwr2thepeople (1)

Previous in Forum: Method Statements for Oil-Filled Transformers   Next in Forum: Connecting a Generator in Parallel

Advertisement