380 VAC Induction Motor

02/03/2009 5:43 AM

1.What cause three phase 380v AC induction motor burn?Megatest shown only two phase shorted.Please advise.Thanks in advance.

2.How a solid state starter protect three phase 380v AC induction burn?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: AC Induction motor

02/03/2009 7:27 AM

<1.What cause three phase 380v AC induction motor burn?>

Too much current. The overload protection unit at the motor starter was set too high.

<2.How a solid state starter protect three phase 380v AC induction burn?>

The electronic overload needs to be set to the full load current of the motor. If it is set higher, then there is nothing to prevent a repeat occurrence.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#2

Re: 380 VAC Induction Motor

02/03/2009 10:54 PM

i am fuuly agree with other answar also but pls check following also.

01. Any mechnical failure like bearing etc.

02. Is there any single phase preventer in circuit.

Register to Reply Off Topic (Score 5)
Anonymous Poster
#3

Re: 380 VAC Induction Motor

02/04/2009 12:56 AM

First let me know few things

  • Whethere this motor is earlier rewinded?
  • what type of load connected to this motor, i.e. application?
  • What is the voltage you are feeding to this motor through starter?
  • What was the O/L set and what is the current drawn by the motor on load?
  • what is the FLC of the motor?

probably with clarification of these points we can make out something

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: 380 VAC Induction Motor

02/04/2009 1:34 AM

1. There are literally dozens, if not hundreds, of reasons why a motor may "burn", and even the term "burn" can mean a large number of things. Over current is the most likely, but certainly bad bearings, high harmonics, poor insulation, voltage spikes, high ambient heat, water intrusion etc etc etc are all valid.

2. Not all Solid State SStarters are the same, in fact some provide NO protection. That is a question only the manufacturer of the starter can answer.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#5

Re: 380 VAC Induction Motor

02/04/2009 4:45 AM

1. Heat. This can be caused by:

(i) overloading or 'pushing' current by overvolting, effect is overall lacquer discolouring where heat is localised. Inadequate cooling or too high ambient temperature could also cause excess heat.

(ii) Winding insulation failure by shorting due to insulation breakdown and poor segregation/untidy arrangement in manufacturing causing short circuit.

2. As far as I know, this only provides motor load current protection and so if 1. is caused by overload it can help protect the motor

__________________
Something new every day!
Register to Reply
Anonymous Poster
#6

Re: 380 VAC Induction Motor

02/04/2009 2:14 PM

I had a this problem a few yrs ago and I installed a over-curnt potctor to stop the in rush of curent. Ther are systems avalble that can monator load and spiking.

Aaron

ht3captin@gmail.com

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#7

Re: 380 VAC Induction Motor

02/06/2009 10:46 PM

what is the stator connection. It must be delta .Most probable reason could be single phasing.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#8

Re: 380 VAC Induction Motor

02/18/2009 7:50 AM

You will find some great explanations of motor failure modes available from Sprecher and Schuh including colour photos of damaged windings and why it happened. Try their website.

Solid state motor protection relays are used to protect motors more accurately than older means. Some solid state starters (softstarters or VSDs) incorporate this quality of protection some don't. Once again the S&S site will help. Also Google GE Multilin and Merlin Gerin Sepam.

Two phases shorted, depending on shorted to what is often due to single phasing.

Register to Reply
Register to Reply 8 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Emjay4119 (1); JRaef (1); MalcolmK (1); nesubra (1); PWSlack (1)

Previous in Forum: Full Load Current   Next in Forum: Cold Cathode Flourescent Lights (CCFL)
You might be interested in: AC Motors, Burn-in Test Equipment, Induction Heaters

Advertisement