PLC Outputs - Module Issue

02/04/2009 1:57 PM

Dear all,

We are using S5 PLC for one m\c.When we start up the m\c after power shutdown.Outout module in the no Indication one output module in the CPU.Then we turn off the power and On in the CPU.we able to get all indication in the output module.I want to solve the problem permenantly.so can u help to give solution for the problem.Is it problem in software(PLC program) or Hardware(Output module).Please give solution

Register to Reply
Pathfinder Tags: PLC PROBLEM
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Engineering Fields - Mechanical Engineering - BSME Clarkson University 1992 Engineering Fields - Software Engineering - BSME Clarkson University 1992 Fans of Old Computers - TRS-80 - DataRock 1.0

Join Date: Apr 2008
Location: Troy, NY
Posts: 388
Good Answers: 3
#1

Re: PLC Outputs - Module Issue

02/04/2009 5:46 PM

Hi Paramasivan4u,

Siemens Simatic S5 PLC?

I'm profiling, since outside the U.S., Siemens used to be the big global PLC player (around 2001 - vs. Allen-Bradley), and I think may still have a bigger global market share than Rockwell Automation.

- Larry

Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#2

Re: PLC Outputs - Module Issue

02/05/2009 2:05 AM

Hi there,

If you have to re-cycle the power on your PLC, especialy Siemens S5, then it sounds as if it a software issue.

You will need the Com software to check the setup of the PLC i.e. does it retain flags and that sort of thing. You will also need to check the user program, as it sounds as if there is something that is being retained, again I would guess a flag, but might be in a DB.

Good luck.

Craig

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#3

Re: PLC Outputs - Module Issue

02/06/2009 1:52 AM

Paramasivan4u,

Frequently, the I/O module needs to be powered on before the CPU, so the CPU will recognize its presence and properly address it. I have had this problem with Siemens analog modules in a remote I/O rack. The symptoms you state sound like this.

With some modules, the program has to write configuration data to the module. In this case, you can possibly use a time delay based on the first pass bit, to wait a second or so before writing this configuration data. If all else fails, you may have to find a way to get the rack powered before the CPU.

Troubleshooting can lead to the engineer's version of "male pattern baldness", with hair being pulled out in clumps! However, persevere, and I believe you will find and fix it.

Regards--JMM