Temperature and Electricity in AC Systems

02/06/2009 1:27 AM

Dear experts,

Is there any corelation between setting temperature in AC system and its electrical consumption.

If we reduce the AC setting point , ie from 22 to 23 Degree Celcius, how much KWH / electricity consumption can be saved theorically .

thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Temperature VS electricity

02/06/2009 6:20 AM

It depends on the system and the losses in it.
Say you are heating up a tank of liquid to that temperature...once the liquid is up to temperature, if none is used and no heat escapes then very little extra power will be required.
If however the tank isn't insulated and liquid is constantly being drawn off and replaced with cold liquid then lots of power will be rquired.

So hopefully you see we don't have enough information to answer the question.

The best way in these situations is to measure it as there are often too many variable to make a meaningful calculation.

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#2

Re: Temperature and Electricity in AC Systems

02/07/2009 12:38 AM

As you are raising set point of AC from 22 to 23 deg C, effectively you will need less Kcal equivalent to Effective mass being cooled X effective equivalent specific heat X 1 (Deg).

Thus the equivalent electrical energy considering efficiency of AC system will be saved.

Obviously, to find out the effective mass and effective equivalent specific heat is very difficult. Best (and only) way is as Del say, measure practically, at same environment.

Register to Reply
Commentator

Join Date: Mar 2008
Location: Strongsville, Ohio USA
Posts: 62
#3

Re: Temperature and Electricity in AC Systems

02/08/2009 10:50 AM

Yes there is a correlation between thermostat settings and power consumed. ASHRAE manual J provides heat load and cooling load formulas for various types of residential construction materials. Result is in BTU/H which can be converted to watts. The design indoor air temperatures can be varied and the difference Will be the amount saved. The smaller the temp difference between indoor and outdoor air the less power consumed.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#4

Re: Temperature and Electricity in AC Systems

02/08/2009 12:00 PM

Yes the relation exists ; for example we are in hotel industry recording on a daily basis the outdoor max and min temprature and based on that we are calculating the monthly heating and cooling degrees.

If the load is constant ; of course the heating and the cooling degress along with the set point will contribute affecting the electricity power consumptions.

We are monitoring that trough the daily KWHr readings compared to the heating/cooling degrees and the set point of our chillers.

Files are vaialbe for share.

ESMAT

Register to Reply
Commentator

Join Date: Apr 2008
Posts: 71
Good Answers: 4
#5

Re: Temperature and Electricity in AC Systems

02/09/2009 4:08 AM

For central hydronic heating systems in Germany, there is a rule of thumb: If the set temperature (in the room) is lowered by 1 degree C this will result in approx. 6 % savings in heating energy.

I would guess that the relation should be more or less the same if you apply this rule to AC systems (I suppose moderate differences between indoor and outdoor temperature?). Of course, the figures may change dramatically with the quality of the insulating of the building (including windows!!), the heat gain through solar radiation and the efficiency of the AC system. Are you talking about a central AC or a number of single-room units?

regards nudnik

Register to Reply
Active Contributor

Join Date: Jan 2008
Posts: 17
#6
In reply to #5

Re: Temperature and Electricity in AC Systems

02/09/2009 4:37 AM

Thanks Nudnik,

That's what I am looking for. Rule of thumb

btw, term of " 6 % saving in heating energy", Could it be meant 6 % saving of AC's electrical usage ??

or maybe you have another conversion factor to convert it into KWHour.

I am talking about both AC you mentioned above. Trying to get saving by increase seting temperature of AC.

thank you

Register to Reply
Associate

Join Date: Jan 2007
Posts: 42
#7
In reply to #6

Re: Temperature and Electricity in AC Systems

02/09/2009 12:29 PM

It is dependent on the outdoor air conditions. The losses through cracks, windows, walls, etc are greater the greater the temperature differential between your indoor system and outdoor system. Losses in the same house in 75F Los Angeles will be much different than 40F Seattle.

Register to Reply
Commentator

Join Date: Apr 2008
Posts: 71
Good Answers: 4
#8

Re: Temperature and Electricity in AC Systems

02/10/2009 4:36 AM

Hi Adrian,

as the other contributers have already mentioned, it is not possible to give reliable figures, without having knowledge of tyical outdoor temperatures, the thermal insulation standard of the room or house, the way you (in person) operate the AC system and so on. I have a pfd document published by toshiba in which they give some figures on relative energy consuption of their inverter AC systems compared to fixed speed AC systems. Unfortunately, the brochure is written in german and I do not know if a corresponding publication is available in english. The quote that the energy saving potential ist 4 % of the power input (electrical energy) per 1 degree C higher room temperature or setpoint temperature. But as far as I read this brochure this figure is only related the their inverter AC systems.

I would be happy to send you the pdf (with just a few annotations in english ) if you do not mind to provide me with an e-mail adress. Sorry, I do not know if it is possible to upload a pdf to this forum

nudnik

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adrian (1); Anonymous Poster (1); ckartson (1); gsuhas (1); nudnik (2); spencer (1); user-deleted-1105 (1)