Fault Current Ratings

02/10/2009 11:22 AM

Guys, I'd like to know how to calculate the max fault current for an 11kv transformer if one knows that the power output is 10.9mVA?

Elp.

Register to Reply
Pathfinder Tags: Fault Current power
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: Fault current ratings

02/10/2009 11:28 AM

What's the transformer impedance? I = V/Z

Fault current ratings (as in NEMA, NEC, ASTM, NFPA or UL) are one thing, and actual fault currents (hopefully less than rating) are another.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Member

Join Date: Oct 2008
Location: UK
Posts: 8
#2
In reply to #1

Re: Fault current ratings

02/10/2009 11:53 AM

Wow that was quick! I was going to assume 80% of max 'nominal' fault rating as a likely fault but how to calc the max fault to begin with?

Is there a 'typical' impedance value one can use as an assumption..... 5% Voltage?

Register to Reply
Associate

Join Date: Feb 2009
Location: Bluegrass Country of Kentucky
Posts: 29
Good Answers: 1
#3

Re: Fault Current Ratings

02/10/2009 12:44 PM

You need to find the multiplier for that transformer. Take 100/%Z of the transformer. Then to find the maximum available fault current on the secondaries of the transformer, multiply the full load rated current of the transformer by the Multiplier above. In other words the multiplier for a 5% transformer impedance would be 100/5= 20. So the maximum fault let thru current (based upon an infinite bus on the primary) would be the FLA X 20. Best source to read up on this is the Bussman handbook.

__________________
Joe the Electrical Contractor to the EOR, I know it was suppose to be in my base bid, but I still am going to submit a change order for it.
Register to Reply Score 1 for Good Answer
Member

Join Date: Oct 2008
Location: UK
Posts: 8
#4
In reply to #3

Re: Fault Current Ratings

02/11/2009 3:46 AM

So, is it....?

1.732 / V (11kV) / 10.9mVA = 572A as its working load..... then x 20 = 11.4kA max fault current

Assuming a 5% impedance (100/5=20). It looks about right.

Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#5

Re: Fault Current Ratings

02/11/2009 9:00 AM

Consult "Ugly's" page 51

Register to Reply
Member

Join Date: Oct 2008
Location: UK
Posts: 8
#6
In reply to #5

Re: Fault Current Ratings

02/11/2009 9:35 AM

Hi GHOG,

'Ugly's?? unfortunately, I don't have a copy....what is it?

Excuse my ignorance, I'm a mechanical bod who has been forced to dabble in this stuff that you can't see...called electricity!!...nasty stuff with loads of calcs every left, right and centre!!!

Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#7
In reply to #6

Re: Fault Current Ratings

02/11/2009 9:45 AM

Ugly's Electrical Reference

Burleson Distributing Corp.
3501 Oak Forest Dr
Houston, TX 77018
800.531.1660
www.uglyselectrical.com

Register to Reply
Member

Join Date: Oct 2008
Location: UK
Posts: 8
#8
In reply to #7

Re: Fault Current Ratings

02/11/2009 10:02 AM

Thanks ol' goat, I'll pop an order into amazon.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bill (1); Electron Plumber (1); GRAY HAIRED OLD GOAT (2); user-deleted-1092 (4)

Previous in Forum: Electric Motor Efficiency   Next in Forum: Isolator Switch Rating

Advertisement