what is the difference between bus coupler circuit breaker and switched busbar circuit breaker? Where are we using them generally? Thank you for any advices.
Re: IEC60050-605-02-40 and 41
02/11/2009 12:58 AM
The bus coupler circuit breaker is coupling two bus section and make one common bus if either one source of supply available or two supply syncronized supply available to share the heavy load. if bus coupler circuit breaker open two source will feed load separately.
The difference between two is switched busbar circuit breaker will be eaither as source or load breaker in "T" connection
02/11/2009 1:02 AM
Bus coupler connecting two end to end bus
switched cb connecting in T coonection
it is used in case more than one source of supply.