In "Segregated Bus Duct" the 3 phases are partitioned in one duct.

In "Non Segregated Bus Duct"the 3 phases are in one duct but not partitioned.

Are the above two statement correct?

Register to Reply
Pathfinder Tags: Bus Ducts
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Medium Voltage Bus Ducts

02/10/2009 6:13 PM

If I'm reading your mind correctly the answer is yes if by duct you mean wireway, cable trough, etc. Doesn't have to be three phase either, although that is what we use it for typically.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#2

Re: Medium Voltage Bus Ducts

02/11/2009 10:27 AM

Hi, parvez hassan, and welcome to CR4!

You are correct. "Segregated" and "non segregated" have very specific meanings when referring to MV bus duct. There is also a third type, "Isolated Bus Duct", where each phase conductor is in its own separate metal clad enclosure. For more details, please see http://www.electricity-today.com/et/issue0403/mediun_voltage_bus_duct.pdf.

__________________
Experience: The knowledge you gain just AFTER you needed it.