Cooling Tower water consumption

02/10/2009 4:23 PM

I would like to know the formula to calculate the water consumption or water being evaporated in cooling tower with respect to the entering and leaving water temperature, ambient air wet bulb temperature and flow rate. SI unit if possible.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jan 2009
Location: Western Canada
Posts: 295
Good Answers: 51
#1

Re: Cooling Tower water consumption

02/10/2009 5:32 PM

Do the basics here help you?

http://spxcooling.com/pdf/ctII-1.pdf

__________________
A little knowledge is a dangerous thing.
Register to Reply
Member

Join Date: Jan 2009
Posts: 8
#2
In reply to #1

Re: Cooling Tower water consumption

02/10/2009 6:17 PM

Thanks

Register to Reply
Anonymous Poster
#3

Re: Cooling Tower water consumption

02/11/2009 6:04 PM

Evap Rate GPM = (water in temp degf-water out temp degf) * Recirc Gpm /1,000

See www.expertctr.com/ch_12.php

Register to Reply
Member

Join Date: Jan 2009
Posts: 8
#4
In reply to #3

Re: Cooling Tower water consumption

02/11/2009 8:25 PM

Thanks. It's great but I may have missed some diagrams. There is a blank section in the middle.