Knee-Point Voltage

02/11/2009 5:48 AM

Kindly suggest how to decide the knee point voltage.

The case in discussion is that of an 11kV Switchgear.

Outgoing Cable feeder CT core for B/B protection is rated for 3500Amps, CL.PX.

Can we consider a knee point voltage of >500V?

Thanks for your help in advance

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Feb 2009
Posts: 35
#1

Re: Knee-Point Voltage

02/11/2009 8:01 PM

To roughly estimate the required Ek=2(If/N)r, where If=Switchgear Fault current rms(normally 20kA), N=turns ratio (Ip/Is), r=rough estimate of CT secondary resistance (10A=0.1ohms, 5A=1ohms, 1A=10ohms)+connection conductor loop resitance= 0.006ohms/m.

For an 11KV switchgear CT the Ek can be based on a rough rule of thumb of 0.4v/Ts & at N of 1/350(10A sec)=140v, 1/700(5A)=280v, 1/3500(1A)=1400v.

See IEC60044-1, 14.4 for CT Ek etc.

Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#2
In reply to #1

Re: Knee-Point Voltage

02/12/2009 9:44 PM

Small correction: the limiting condition is Ek≥2(If/N)r; other thing is as above.

thanks.