First, Why do you think capacitors need to be installed "in panels"?
Good Answers: 103
Re: capacitor bank
02/16/2009 11:20 PM
may be in some instrument PCB's ?
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member
Good Answers: 42
Re: capacitor bank
02/17/2009 9:26 AM
The basic requirement of capacitance bank in LT panel is your question, I presume.
Majority of industrial load is inductive and that results in low PF . If the PF is not corrected there will be large KVAR (reactive power) that results in loss of power. If the PF is low most of the power companies charge Low PF penalty . To avoid all these capacitor banks are installed with large induction motors and induction heating equipments and in substations to improve PF . The selection of capacitance bank depends on the actual power factor of your system and actual amount of correction . You have to decide weather you need individual compensation near load, Group compensation or compensation centrally. The decision is highly technical job and need real practical experience.