PLC Logic - Interlock and Permissive

02/20/2009 1:52 AM

Colleagues

Anyone out there who can differentiate clearly the difference between interlock and permissive. This is referring to the use of these terms in PLC logic. Some logic have have got ready conditions, then permissive conditions and then interlock. Any standard out there which guides the use of these terms in PLC coding?

Thank you indvance

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Weaponology - New Member Netherlands - Member - New Member Fans of Old Computers - Commodore 64 - New Member

Join Date: Sep 2007
Location: Japan
Posts: 2703
Good Answers: 38
#1

Re: Controls Engineering

02/20/2009 3:50 AM

I am not a wiz on PLC's maybe this link is of use

http://forums.mrplc.com/index.php?showtopic=15832

__________________
From the Movie "The Big Lebowski" Don't pee on the carpet man!
Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#2

Re: PLC Logic - Interlock and Permissive

02/23/2009 2:29 AM

Hi there,

To put this simply - a Premissive is something you need in place to start a machine i.e. a switch must be closed. Once the machine is running you do not care anymore what state this switch is in or changes to.

An Interlock on the other hand is different. It is also known as a Trip. You do care about what state the Interlock is because if it changes you will trip your machine if it was running.

For more information about the terminology and standards try www.isa.org

Regards,

Craig

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #2

Re: PLC Logic - Interlock and Permissive

03/14/2014 5:12 PM

I think it's simpler than that, also, interlocks are applicable beyond trips.

A Permissive is something that must take place BEFORE another action or sequence of actions can be undertaken.

An Interlock is something that takes place as a RESULT of or as PART of another another action or sequence.

For example a latched Emergency Stop button would be a Permissive: the logic must be true (high, on) before anything else can take place, and must REMAIN true for the entire time, "permitting" the process to proceed.

If I have Start button going to a motor starter, which also has an Auxiliary Contact to indicate that the contactor has closed, the Start is a Permissive, the Aux. contact is an Interlock that I can use to seal-in around the Start button. So in this case the Permissive enables the action to begin, but the Interlock then takes place and allows it to continue after the Permissive is no longer necessary.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Participant

Join Date: Mar 2014
Posts: 1
#3

Re: PLC Logic - Interlock and Permissive

03/14/2014 4:31 PM

Do you check interlocks before starting the equipment or are they checked only after the equipment has already started?