When should i use MCCB and MCB Breakers?

02/20/2009 1:12 AM

When should i use Molded Case Circuit Breakers and Mini Circuit Breakers?

what is the smallest Ampere rating of a breaker should i use for a motor without tripping it during starting and should i use MCCB or MCB, Pls. help

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#1

Re: When should i use MCCB and MCB Breakers?

02/20/2009 4:13 AM

Dear Friend,

Trying to answer your question as :-

When should i use Molded Case Circuit Breakers and Mini Circuit Breakers?

* First of all MCB is Miniature Circuit Breaker , since it is miniature it has limitation for S C and Amp Rating Both.

# MCB are available as Singe module and used for :-

Number of Pole :- 1,2,3,4 - 1+ N , & 3 + N

# Usually Current range for A.C., 50-60 HZ ., are from 0.5 Amp - 63 Amp.

Also available 80A, 100A, and 125 Amp.

# SC are limited 10 KA

# Applications are as :- Industrial , Commercial and Residential application.

# Tripping Curve

B Resistive and lighting load

c Motor Load

D Highly inductive load.

* MCCB :- Moulded Case Circuit Breaker

# MCCB are available as Singe module and used for :-

Number of Pole :- 3 pole , & 4 Pole

# Usually Current range for A.C., 50-60 HZ ., are from

3.2 /6.3/12.5/25/50/100/125/ 160 Amp. - SC 25/35/65 KA

200 250 Amp. - SC 25/35/65 KA

400 630/800 Amp - SC 50 KA

# Protection release :-

Static Trip :- Continuous adjustable overload protection range 50 to 100 % of the rated current

Earth fault protection can be add on with adjustable earth fault pick up setting 15 to 80 % of he current

# Micro processor Based release :-

Over load rated current 0.4 - 1.0 in steps of o.1 of ln trip time at 600 % Ir(sec) 0.2.0.5,1, 1.5 , 2 ,3

Short Circuit :-2 - 10 in steps of 1 lr , short time delay (sec) 0.02.0.05,0.1, 0.2 ,0.3

Instantaneous pick up ;- 2 - 10 in steps of 1 ln Ground fault pick up Disable, 0.2 - 0.8 in steps of 0.1 of in

Ground fault delay (sec) - 0.1 -=to 0.4 in steps of 0.1

This are available with communiction port RS 485 and protocol MODBUS,RU

THE ABOVE INFORMATION CAN VERY WITH DIFFRENET MANUFACTURER

HOPE YOUR QUERRY HAS BEEN TRIED TO ANSWER WITH IMMEDIATE AVAILABLE INFORMATION

NIRANJAN A SHATSRI

Reply Good Answer (Score 3)
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#2
In reply to #1

Re: When should i use MCCB and MCB Breakers?

02/20/2009 8:52 AM

Hi Niranjan,

You have explained very well in a language which a technical person can understand . Now MCCB is available up to 1600 amps rating also. Due to its compactness they are replacing ACBs even for high capacity switching. There are many threads in CR4 on the same subject.

Good Answer.

Reply
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#3
In reply to #1

Re: When should i use MCCB and MCB Breakers?

02/21/2009 11:28 PM

GA

__________________
Atlas Shrugged - JGD
Reply
Participant

Join Date: Mar 2009
Posts: 3
#4

Re: When should i use MCCB and MCB Breakers?

03/05/2009 11:07 AM

Let me add - on

In choosing MCCBs VS MCBs, its not just the rating, its also about discrimination.


well discriminated breaker configuration will ensure that 1 branch trips without affecting another branch, thus ensuring continutity of power supply

Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#5
In reply to #4

Re: When should i use MCCB and MCB Breakers?

03/06/2009 3:43 AM

Let me add - on

In choosing MCCBs VS MCBs, its not just the rating, its also about discrimination.


well discriminated breaker configuration will ensure that 1 branch trips without affecting another branch, thus ensuring continuity of power supply

DEAR FRIEND,

WHAT DISCRIMINATION R U REFERING ?

I THINK YOU ARE REFEERINGABOUT DISCRIMINATING THE FAULT .

WHICH BRANCH ?

ARE YOU TALKING ABOUT VARIOUS FEEDERS CONNECTED TO VARIOUS LOAD ?

THE DISCRIMINATIONS ARE CO ORDINATED WITH SELECTION OF RATING FOR S.C./ O.C/ E.F.C ETC., WITH PROTECTIVE RELAYS. AND RATING OF FEEDER RECEIVING OF POWER FOR DISTIBUTION TO GROUP OF FEEDER WITH SAY X - AMP , THAN THE UP STERAM FEEDER RATING ARE WITH > THAN THAT RATINGS AND SETTINGS OF PROTECTION ARE BEING CO ORDINATED ACCORDINGLY , THE OUT GOING FEEDERS RATINGS ARE < THAN THE FEEDER RECEIVING POWER AND CONNECTED AS IN COMING TO THE BUS.

THE SAME WAY S.C /FAULT CURRENT RATINGS SHOULD BE RATED < TOWARADS MAIN IN COMING FEEDER TO OUT GOING FEEDERS AS PER S.C OF RESPECTIVE FEEDER LOAD.

ANY QUERRY R APPRECIATED AND CAN BE DISCUSSED BY CASE STUDY IF YOU HAVE SPECIFIC DISTRIBUTION NET WROK TO DESIGN.

REGARDS N THANKS.

nascon

Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Current Maarey (1); nascon (2); V.I.Abraham (1); wahkao (1)

Previous in Forum: Transformer Inrush Current   Next in Forum: PLC Logic - Interlock and Permissive
You might be interested in: Circuit Breakers, Load Centers, Circuit Tracers

Advertisement