Switchyard Protection

02/20/2009 9:24 PM

What is stub protection in one and half breaker scheme.

Register to Reply
Pathfinder Tags: Switchyard Protection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#1

Re: Switchyard Protection

02/25/2009 4:22 AM

Background:

In a recent trends, the power stations have 200/400 KV outgoing line arranged in a one and half scheme breakers.

Meaning there are 3 breakers per two outgoing lines i.e 1.5 breaker per line.These breakers are connected on two buses,main bus-I and Bus-II.

When one of the line ( say-1) is tripped breakers 1-52CB and 2-52 CB trips.Then line is isolated i.e isolator 1-89, 1-89A,2-89A and 1-89L is opened, that side becomes dead (or known as Stub).Isolator 2-89B is not opened as line -2 OR (Transformer T/F-1) is in service.

Now the area between ( 3-52CB & T/F-1 and 2-52CB i.e Stub or dead end) is protected by "Stub" protection on 3-52CB side which gives bus overcurrent trip if the line isolator is opened and the current exceedes pre-set value.

nascon

Register to Reply Score 1 for Good Answer
Member

Join Date: Jan 2009
Location: Baroda
Posts: 7
#2
In reply to #1

Re: Switchyard Protection

03/03/2009 5:14 AM

Is it a Line feeder protection only?

How this protection is provided in one and half breaker scheme.

Register to Reply
Anonymous Poster
#3

Re: Switchyard Protection

02/07/2011 1:21 PM

Yes It's used for line only.When line isolator is open and a fault is present between CT and Line isolator, Trip command is issued to the line breaker.

Register to Reply Off Topic (Score 5)
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ankur_Elect (1); Anonymous Poster (1); nascon (1)

Previous in Forum: High Voltage X-Ray Generator   Next in Forum: Generating 50 HZ

Advertisement