02/24/2009 11:35 PM
Can anyone write back if Starting PF & No Load PF of Motor is same with detail clarification.
BNDas
Re: Starting PF & No Load PF of Motor
02/25/2009 9:30 AM
No, they are not the same. A motor can have a varying power factor. The starting power factor on an standard induction motor will be the same for locked rotor power factor. No load power factor is when there is no load on the shaft. Both can be low, but they will not be the same. A motor sees its best power factor at its full load rating by design.
Joe the Electrical Contractor to the EOR, I know it was suppose to be in my base bid, but I still am going to submit a change order for it.
02/25/2009 11:50 AM
Power factor is not a static value.
It states the timing relationship between the voltage and the actual current flow, which fluctuates wildly at times. Especially when starting a motor, which actually reverse generates as it begins to rotate, and reaches rated speed when the forward/reverse values equalize.
Keeping it simple. CJM
I do not 'know it all', but i will admit that I would like to. CJM