Conduit Runs and Pull Boxes

02/24/2009 9:57 PM

What is the maximum 3/4" emt conduit run before a pull box is required? I have looked through the Canadian Electrical Code to no avail, hopefully someone can remember or steer me in the right direction, Thanks

__________________
If you say you can't do something, you'll be right
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: What is the maximum 3/4" emt conduit run before a pull box is required?

02/24/2009 10:03 PM

That is not in the NEC. It is more a design issue.

Register to Reply
Active Contributor

Join Date: Feb 2009
Location: Beautiful British Columbia
Posts: 12
#2
In reply to #1

Re: What is the maximum 3/4" emt conduit run before a pull box is required?

02/24/2009 10:13 PM

Thanks, that would explain why I couldn't find it. I have always used a number of 200' as a rule of thumb for my installs but just wanted to find if it actually said it anywhere.

__________________
If you say you can't do something, you'll be right
Register to Reply
Power-User

Join Date: May 2007
Location: 39°10' N 91°52' W
Posts: 237
Good Answers: 15
#3

Re: What is the maximum 3/4" emt conduit run before a pull box is required?

02/25/2009 6:46 AM

The only thing I have ever found in the NEC concerning pull boxes is the maximum turns. I also have used that 200' rule of thumb, and never had an install fail inspection for this.

__________________
If you don't have time to do it right the first time, when are you going to have time to do it over?
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#4

Re: What is the maximum 3/4" emt conduit run before a pull box is required?

02/25/2009 8:34 AM

ricky t; usually the lenth of your fish tape. perry

Register to Reply Score 1 for Good Answer
Member

Join Date: Feb 2009
Posts: 5
#6
In reply to #4

Re: What is the maximum 3/4" emt conduit run before a pull box is required?

02/26/2009 1:30 AM

I have a 600' fish tape, not a good answer

Register to Reply
Power-User

Join Date: May 2008
Location: Olympia, WA
Posts: 125
Good Answers: 5
#10
In reply to #4

Re: What is the maximum 3/4" emt conduit run before a pull box is required?

02/26/2009 11:09 PM

Greetings.

I agree. That is what I was thinking as I read down the list. Usually 10 feet less than length of fish tape if possible. Fish tapes usually come in 50 ft, 100 ft, and 200 ft.

Register to Reply
3
Associate

Join Date: Feb 2009
Location: Bluegrass Country of Kentucky
Posts: 29
Good Answers: 1
#5

Re: What is the maximum 3/4" emt conduit run before a pull box is required?

02/25/2009 9:28 AM

Per the NEC, you have to hit a j-box if you have gone thru the equivalent of four 90 degree bends or if you believe that the pulling tensions to install the planned wire in the conduit will result in damage to the wire. So best way to determine is to look at the manufacturer's recommended maximum pulling tension and then with tension pulling calcs in hand, figure out where in the pull you need to assist in pulling the wire. Hope this helps.

__________________
Joe the Electrical Contractor to the EOR, I know it was suppose to be in my base bid, but I still am going to submit a change order for it.
Register to Reply Good Answer (Score 3)
Anonymous Poster
#7

Re: Conduit Runs and Pull Boxes

02/26/2009 5:48 AM

I have used a plastic baggie and a vacuum cleaner to pull a leader through very long runs of conduit,300 feet or more(usually underground).Works great.I don't recall seeing a specified maximum length, but usually put on every 100 feet for convenience sake.

Register to Reply
Commentator

Join Date: Oct 2007
Location: Caribbean
Posts: 79
Good Answers: 2
#8
In reply to #7

Re: Conduit Runs and Pull Boxes

02/26/2009 7:51 AM

Hey Guest,

I know he original post concerned the length of 3/4' conduit between pull boxes .I am from the Caribbean, we do have a local electrical code which specifies a maximum of three 90 degree bends and 120 feet of conduit between pull boxes.

But the idea of using a vacuum cleaner and a plastic bag to pull in a pull-line is a very unique idea.

For small conduit up to 1" , I normally use a very light nylon line tied to a small ball of styrotex blown by compressed air.. For large conduit up to 4" , I use a plastic pop bottle tied to the nylon line. Works great too.

Is there any other great suggestions which may benefit us all.

Just my 2 cents worth.

__________________
Learn more, Do more , Be more
Register to Reply
Associate

Join Date: Nov 2007
Posts: 50
#9

Re: Conduit Runs and Pull Boxes

02/26/2009 9:07 AM

NEC rules trump all, but in addition to that I use a program call "Pull-Planner 2000". It is available from American Polywater. Works well. Saves sleepless nights wondering if I have gone too far with my pulls. I think it costs $99. Worth every penny.

Register to Reply
Power-User
Engineering Fields - Systems Engineering - Member for some time now, see my profile.

Join Date: Aug 2007
Location: Essex, UK
Posts: 364
Good Answers: 3
#11

Re: Conduit Runs and Pull Boxes

02/27/2009 3:59 PM

From Sleepy,

Whatever length of pull through that you achieve; it will be dependent upon the thickness of the cable and the type of cable that you are trying to pull through. Also I have found in practice that you can obtain slippery stuff to coat the cable with and this aids the pull capability considerably.

Years ago, the ointment of choice was called Hellerman oil, we used to use this for small cables in confined spaces; I do not know whether this is available nowadays but you can purchase Ideal, Yellow 77 Wire pulling lubricant which is more appropriate for pulling cables through conduit; I have used it for many years. Made in the USA but I bought it locally here, in the Uk, at my local Electrical Wholesaler.

Good Luck

Sleepy

Register to Reply
Member

Join Date: Feb 2009
Posts: 5
#12

Re: Conduit Runs and Pull Boxes

10/05/2011 1:09 AM

As a general rule we go 200 feet, the state many years ago enforced the 200 foot, today it depends on the pulling force for each type and size of wire. You can have no more than 360 degrees in a conduit run with out a box or pulling body. the program from the pulling lube companys work great.

Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); charlie_r (1); djacob (1); Electron Plumber (1); NoEngr (1); OlympiaWA (1); perry (1); Ricky T (1); Sleepy (1); Themonster (2); wareagle (1)