how can calc

02/25/2009 7:19 AM

HI

i need to know

how can i calc. trnasformer capacity 20kvto 400v

if i have FLA , RLA , and starting ampe

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Feb 2009
Location: Bluegrass Country of Kentucky
Posts: 29
Good Answers: 1
#1

Re: how can calc

02/25/2009 9:37 AM

In the US, you need to use the FLA (full Load Amps) to size the transformer. It needs to be a minimum of 125% of the FLA of the largest motor, plus all the other motor FLAs added up. Then KVA is just Volts X Amps X square root of 3 for three phase circuits. Keep in mind, 125% is just for the US under the NEC. Other countries may have a different approach.

__________________
Joe the Electrical Contractor to the EOR, I know it was suppose to be in my base bid, but I still am going to submit a change order for it.
Register to Reply
Active Contributor

Join Date: Jul 2008
Posts: 12
#2
In reply to #1

Re: how can calc

02/26/2009 5:06 AM

Thanks so much