Current carrying capacity of a conductor in AC & DC

02/28/2009 4:17 AM

Hi to all:

what will be the current carrying capacity for a copper conductor in case of:

1. AC current

2. DC current

if there is difference, why? please response me.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#1

Re: Current carrying capacity of a conductor in AC & DC

02/28/2009 4:42 AM

What is current carrying capacity?

depends on what material? where are you using? underwater? underground? in air? or in vacuum? at what ambient? and many mother factors.

and also what quality are you looking for?

There is a difference due to skin effect. How much? depends on frequency of AC Current.More is frequency lesser is the ability.

What is skin effect? Google--------

Reply
Anonymous Poster
#2

Re: Current carrying capacity of a conductor in AC & DC

02/28/2009 7:04 AM

Generaly speeking the DC current needs almost the same cross section as the RMS AC current needs.Especially at main frequency (60 or 50 Hz ).

Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#3
In reply to #2

Re: Current carrying capacity of a conductor in AC & DC

02/28/2009 8:12 AM

but you need stranded for AC

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Active Contributor

Join Date: Feb 2009
Posts: 10
#4
In reply to #3

Re: Current carrying capacity of a conductor in AC & DC

02/28/2009 8:45 AM

No way . At 60 Hz it's no matter if the wire is solid or stranded ( at the same cross section of course )

Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#5
In reply to #4

Re: Current carrying capacity of a conductor in AC & DC

02/28/2009 11:18 AM

Engineering Electromagnetics-Hayt

"In a power station a bus bar for AC at 60 Hz with a radius larger than 1/3rd of an inch (8 mm) is a waste of copper, and in practice bus bars for heavy AC current are rarely more than 1/2 inch (12 mm) thick except for mechanical reasons.

Skin depth (depth below the surface of the conductor at which the current density decays to 1/e : about 37% of the current density at the surface) is 8.5mm approx for 60 Hz, ie the current(density) at about 8.5mm below surface is only 37% of surface current.

So At 60 Hz it's no matter if the wire is solid or stranded !!!

If its is so, I think there was no reason that we use the stranded wires for all our cables (and also transmission line) Why to waste the $s ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Active Contributor

Join Date: Feb 2009
Posts: 10
#6
In reply to #5

Re: Current carrying capacity of a conductor in AC & DC

02/28/2009 11:47 AM

Thanks for your reply , but we are not talking about "transmission lines" , neither "power stations". The actual discussion is about the home power line , i think. Maybe i'm wrong.

Reply
Power-User

Join Date: Jan 2008
Location: since 20 Jan 09, the USSA
Posts: 375
Good Answers: 81
#7
In reply to #5

Re: Current carrying capacity of a conductor in AC & DC

02/28/2009 12:30 PM

sb is correct as far as large ampacity bus bars go; such busbars are often hollow sections of copper pipe for the very reason he cites. But absent that level of current, what he says is not a definite rule at all. I don't know how they do things in India, but in the USA house wiring is all solid. The reason that power cords for equipment are stranded is flexibility, not ampacity.

The only time stranded cable buys you ampacity over the same cross-section of solid wire is if you are at a very high frequency (pronounced skin effect) and each strand is separately insulated magnet wire. This is called Litz wire, and it forces the current to flow on each and every conductor, instead of just the outside circumference. But that kind of wire is usually reserved for rf circuits, such as reducing the resistance and increasing the "Q" of a tunable loop antenna used at frequencies in the tens of kilocycles to thirty megacycles.

Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#10
In reply to #7

Re: Current carrying capacity of a conductor in AC & DC

03/01/2009 1:02 AM

Note : this is a homework question (that is why no specifice) and i gave a general reply - the effect of the skin effect exixt whether it is bus bar or home wiring.

But in home wiring we are not bothered simply because the

a) length is short so the drop in the effective specific resistance will not be significant.

b) Current carried is small.

c) The conductors are almost universally used at a very high factor of safety.

However it is not only trensmission/ geneartin, in the industries, the machines are also fed by stranded wires for the same reasons and also the earth strip is a flat strip and not a round bar or a rectangular one (not only in the earth pit but also on the areas outside pit).

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Power-User

Join Date: Jan 2008
Location: since 20 Jan 09, the USSA
Posts: 375
Good Answers: 81
#11
In reply to #10

Re: Current carrying capacity of a conductor in AC & DC

03/01/2009 1:22 AM

Sorry, no skin effect in house wiring at 60 Hz. Skin depth in copper is about 8 mm at 60 Hz, and that is much thicker than anything besides the main feeders into the breaker box. And using stranded wire would have no effect on skin depth losses anyway, unless the stranded wires were individually insulated Litz wire (per my original post) which it most certainly is not in house wiring.

Another responder from India, rakesh_semwal , correctly identified the reason for using higher strength steel cores in power transmission lines - for strength, and because of skin effect, the higher resistance steel at the cable center does no harm.

And if the earth strip is flat that is for low inductance, which implies lightning safety issues; at 60 Hz there is no difference in ampacity between a round wire and flat strap of equal cross-section and length.

Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#12
In reply to #11

Re: Current carrying capacity of a conductor in AC & DC

03/01/2009 4:07 AM

no skin effect in house wiring at 60 Hz. Skin depth in copper is about 8 mm at 60 Hz, and that is much thicker than anything The 8mm was already mentioned in my earlier post and the house wiring was already implied in my post (so no dispute there).

For the higher strength steel core - it is correct in AC transmission line and again that is a fact, and here also you are accepting the skin effect.

For eart strip : skin effect is caused by ? (self inductance if I am not wrong) so low inductance of flat strip is correct. And this also do not contradict the statement.

The there is no difference in ampacity between a round wire and flat strap of equal cross-section and length.

correct only for a special case and that is a general home lighting where the fault/normal current do not call for a large conductor size (where skin effect is noticeable)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply Off Topic (Score 5)
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#9
In reply to #5

Re: Current carrying capacity of a conductor in AC & DC

02/28/2009 11:48 PM

Beside current issue stranded wires can have a centre core wire made of some alloy steel to get higher tensile strength.

Reply
Participant

Join Date: Jun 2008
Posts: 3
#8

Re: Current carrying capacity of a conductor in AC & DC

02/28/2009 8:03 PM

They will be the same. The difference will be the voltage drop value as the frequency increase for the ac copper conductor.

Reply
Reply to Forum Thread 12 comments

"Almost" Good Answers: