What is the kVA for This Electrical Appliance?

03/02/2009 12:57 AM

What is kVA for this electrical appliance?

1. 1 hp aircond (3 nos)

2. 2 x 36W fluorescent light ( 13 nos)

3. 150W spotlight ( 6 nos)

4. water pump, 5 hp.

5. Switchboard (panel) c/w ELCB, and MCCB/MCB with 8 nos. female socket. ( 6 nos 16A & 2 nos 32A ). Can anybody estimated the kVA for the MCCB ?

And if i want to use the GenSet for supply, what kVA required for the Genset?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#1

Re: What is kVA for this electrical appliance?

03/02/2009 2:29 AM

What is kVA for this electrical appliance?

first, you must know how much power factor of each device...

and then...

1. 1 hp aircond (3 nos)---> 3 HP =2.23 KW=.............(KVA)

2. 2 x 36W fluorescent light ( 13 nos) =2x36x13= 936 watt = 0.936kW= ........(KVA)

3. 150W spotlight ( 6 nos) = 900Watt= 0.9 KW=.........(KVA)

4. water pump, 5 hp.= 5x0.746 =3.73 KW=............(KVA)

5. Switchboard (panel) c/w ELCB, and MCCB/MCB with 8 nos. female socket. ( 6 nos 16A & 2 nos 32A ). Can anybody estimated the kVA for the MCCB ? depend on Actiatuall load....

now your turn to convert them to KVA, i am sure you can, if you are electrical engineer.....

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2
In reply to #1

Re: What is kVA for this electrical appliance?

03/02/2009 3:29 AM

Why would he ask if he is ? he would have calculated himself.

Next question: what do you mean by power factor ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jun 2008
Location: Malaysia
Posts: 23
#3

Re: What is kVA for this electrical appliance?

03/02/2009 5:05 AM

first of all, what generator you plan to use? a single phase or three phase Generator?

secondly, what pump you are going to use and type of starter 1ph/3ph, DOL/SD/AT?

normally I'll calculate the total connected load and take into consideration the diversity factor ( not all loads operate all the time, right ? ) also must consider what kind of load you plan to connect to the 13 A Sockets, if you estimate full 13A for all 8 sockets, then you will need a big generator.

get me the details and I'll help you.

MultiTech

__________________
There are no Mistakes , Only Lessons.
Register to Reply
Participant

Join Date: Feb 2009
Posts: 4
#4
In reply to #3

Re: What is kVA for this electrical appliance?

03/02/2009 8:48 PM

MultiTech, thanks for your comment.

I plan to use 3 phase Generator.

For the pump, it is 1ph, DOL Starter.

Socket are use for electric drill and power supply for other electrical appliance, spot light, cutter etc. Can you estimate for all loads use all the time and half loads use?

Thanks.

Register to Reply
Active Contributor

Join Date: Jun 2008
Location: Malaysia
Posts: 23
#5

Re: What is the kVA for This Electrical Appliance?

03/02/2009 11:38 PM

based on the info given, a 25Kva 3phase generator should be able to do the work, remember to split the load evenly to all the 3 phases.

regards

MultiTech

__________________
There are no Mistakes , Only Lessons.
Register to Reply
Anonymous Poster
#6

Re: What is the kVA for This Electrical Appliance?

03/03/2009 11:00 AM

1 hp = 746 watts but use .800 kw 2 x 36watts = 72 watts .072 kw 1 x 150 watts =150watts .150 kw 5 x 746 watts = 3,730 watts 3.800 kw total = 4.822 kw x 125% = 6.03 kva for 80% PF Now take the 6 kva and multiply times 125% = 7.5 kva minimum for continuous loads. Generators should not be loaded less than 30% or more than 80% for continuous loads. Most generators have a .8 power factor meaning that the KW rating is 80% of the KVA rating.

Register to Reply
Participant

Join Date: Feb 2009
Posts: 4
#7
In reply to #6

Re: What is the kVA for This Electrical Appliance?

03/03/2009 7:19 PM

Thanks Guest.

How about item no. 5? can you help me to estimate it?

5. Switchboard-3 phase,415Vac (panel) c/w ELCB, and MCCB/MCB with 8 nos. female socket. ( 6 nos 16A-1 phase & 2 nos 32A-3 phase ). Can you estimate the kVA for MCCB ?

Regards,

billy79

Register to Reply