Anonymous Poster

Siemens ET200

03/05/2009 12:43 AM

We have used main siemens plc (s5/135u) with 4 et200 station via profibus network.

there are some cases that profibus connector of one et200 station has been arced and damaged so we loosed all et200's I/O and we had fault signal only on et200.

that et200 station has been installed in 33kv siemens vaccum switch panel to collect vaccum switch signals.

we don't know that should we have 2 seperate earth holes (one for automation system and one for 33kv system).

at the moment there are two different earth bus in panels but all buses will be connected to one earth hole.

Thanks

m.amigh

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Siemens ET200

03/05/2009 1:36 PM

From what you are asking (and describing) it sounds like your earthing system is correct (PLC logic being brought back to a central earthing point preventing ground loops, voltage potential rise issues, etc).

__________________
jack of all trades
Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#2

Re: Siemens ET200

03/06/2009 12:12 AM

Hi there,

Firstly - is it the ET200S or ET200M range? S - is used in substations, while M is used mainly in the plant area.

You have to be very carefull with your earthing of the profibus and the earthing of the actual IM module.

If you RTFM (Read The F#cking Manual) for the ET200 range of cards - you will see that there are two methods for earthing.

What you need to make sure of in either case is that all the ET200 stations share the same earth point i.e. Each M connector must go to the same earth point. You should also make sure that you use the correct Profibus connector as well as the correct Profibus cable (it is usually a purple colour). You also need to make sure that the screen of the bus cable is continous, i.e. the screen must run through all the stations.

You are losing the whole bus - because of you have a floating earth and your screens are not continous. You will have to go and make sure each IM is on the same earth point as well as the screen continous.

Please feel free to download the Profibus standards (for free) from the Profibus web site (there is also a very good user guide that will explain with pictures all of the above) as well as the ET200 manual from the Siemens website (again for free).

If you follow the guidelines - you will have no more problems. The same will aplly to the majority of bus systems.

Regards,

Craig

Reply
Commentator

Join Date: Aug 2011
Posts: 76
#3
In reply to #2

Re: Siemens ET200

08/24/2011 2:19 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Reply Off Topic (Score 5)