plug setting multiplier

03/07/2009 11:40 AM

can someone tell me the exact formula for calculation of Plug Setting Multiplier? I have come across a few and the answers do not match...Please help..Thanks in advance.

__________________
subhasis
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: plug setting multiplier

03/07/2009 11:52 PM

You will have to explain exactly what your are talking about because I have no idea. Plug Setting Multiplier of what?

__________________
jack of all trades
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#2

Re: plug setting multiplier

03/08/2009 12:58 PM

Same response as JoaT from here in the USA... Don't know what kind of device you are asking about, nor setting multiplier of what kind of value?

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Participant

Join Date: Mar 2009
Posts: 2
#3

Re: plug setting multiplier

03/10/2009 1:18 AM

OK. This is the Plug Setting Multiplier of an over current relay I was talking of...please help me out.

__________________
subhasis
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#4
In reply to #3

Re: plug setting multiplier

03/10/2009 11:43 AM

That helps a bit, but we still need to know a lot more!

Sounds like a shunt resistor that carries most of the current, so a low current relay can protect a higher current circuit. But is the shunt directly in parallel with the relay coil, or is there some sensing circuitry? And just what exactly do you want to accomplish? What are the specs of the relay, and what are the specs of the circuit it is to protect? AC, DC, single or three phase, resistive or inductive, etc.?

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Anonymous Poster
#5

Re: plug setting multiplier

07/28/2009 11:46 PM

dear it is the ratio of, fault current of the relay to the pickup value

and pickup value = current setting x secondry current of the CT

Register to Reply Off Topic (Score 5)
Participant

Join Date: May 2007
Posts: 1
#6

Re: plug setting multiplier

10/26/2009 6:52 PM

I Would like to define few terms before explaining you the terms. Normally CT secondary is of either 5A or 1A . Let us consider you are talking about CT with secondary of 5A. Now you have chosen current setting of relay as 150% which means 150% of 5A which is 7.5. Remember 7.5 A now as it is important to remember. Now when there is a fault in the circuit there will be heavy (large) current flow in the circuit. Let us say the current is 5000A in the circuit and let us say you have used the CT of 500/5A as described above as 5A secondary. The 5000 A in primary will be reflected as 5000/(500/5)=5000/100=50 A. Now to find the plug setting multiplier you have to divide 50 A by 7.5 A which is 8. so your plug setting multiplier is 8 and you have to find at which time the relay causes the breaker to trip depending upon the curve with let us say 1 as a time setting multiplier . But if you chose 0.8 as a time setting multiplier you are going to trip faster that is 0.8*time taken when the time setting multiplier was 1. I think you are clear by now regards Rajendra

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: plug setting multiplier

06/07/2010 9:10 AM

Rajendra bhai, thanks for giving the idea of PSM. But it will be really thankfull to you if u can provide some information about Curves. what are all those curves like NI,VI,EI and breif description about relays like IDMT,DT

Register to Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#8

Re: plug setting multiplier

09/18/2013 4:00 AM

PSM = I (relay) / PS

PS : Plug setting.

consider 1.0 A relay (Relay coil is designed to carry current of 1.0 A on continuous basis)

Plug has been set at 0.5 A (50 %)

Fault current : 5 A

PSM : 5.0/ 0.5 = 10

If PSM is less than 1, it means normal conditions

If PSM is greater than 1, Relay is supposed to pick up

Higher values of PSM indicates that how serious the fault is

Register to Reply