Furnace Problems

03/08/2009 3:21 PM

Hi

How to find out the stability of a wall mounted burner furnace.We have a poor flame sensing circuitry in our plant.They are IR based sensors which never worked properly.We are forced to rely on local monitoring and draught profile.Can looking into windbox pressure profile help us predict the furnace stability better.At the same time can anybody deliberate on pulverzed fuel flame blow-off and swirl number significance of a turbulent burner and its relation to wind-box pressure?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#1

Re: Furnace stability

03/08/2009 8:53 PM

You should not operate this furnace outside of the manufacturers required specifications. Certainly, a working flame sensor is an absolute requirement. You risk an explosion, a fire, or at the very least, a compromise of air quality.

The unit should be repaired to 100% working order, or replaced. Anything short of that is putting in risk property, and/or lives.

"We have a poor flame sensing circuitry in our plant.They are IR based sensors which never worked properly."

Your equipment should be brought up to date immediately.

http://hpsweb.honeywell.com/Cultures/en-US/Products/Instrumentation/tempsensors/noncontact/default.htm

Honeywell offers a line of IR sensors that are affordable and very dependable.

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Register to Reply
Commentator
Hobbies - Fishing - New Member but not a new fisherman Hobbies - Target Shooting - New Member

Join Date: Apr 2008
Location: Formerly from NJ USA Planet Earth. Relocated to Space Coast FL
Posts: 79
Good Answers: 9
#2

Re: Furnace stability

03/08/2009 11:35 PM

rajeshmadapati,

The detector circuitry must be replaced. You need IR as well as UV detection. The detectors must be "aimed" properly. IR detectors can get a reading off of hot refractory and allow the fuel to keep dumping into a hot firebox and this is a real invitation for disaster. Several years ago I saw the result of a firebox explosion that caused $300K US in damage. The explosion was caused by 6 gallons or so of #2FO that hit the hot refractory because of a faulty and/or obsolete flame detector. The external walls of the firebox bowed out 17 inches. We were lucky that this firebox had the outer walls "re skinned" recently with a much higher gauge steel. It was nothing short of a miracle that no one got injured or worse and that the plant is still standing. Seeing the aftermath of an event like this once in a lifetime is enough for me. You should replace the system now. Ed

__________________
If you understand no explaination is necessary. If you don't understand no explaination is possible.