Panels, Lines and Loads

03/09/2009 9:55 AM

I got some problem on synchronizing panel but I am not able to understand where the problem is ? Problem is engine not takes loads . Total load of the station is 400amps(200+200)amps.When the engine take to lines with the another two engines then it takes only 45amps loads.At that time another two engine show 220 amps and 500 amps each where the total load 400amps. All the parameters are- voltage-440 v, frequency 50.1 engine cummins make-GTA 1710 (Gas gensets) Alternator-stamford make (380 kva)

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Synchronizing panel

03/09/2009 10:50 AM

Most probably it is engine governor issue. It could be because of the defective governor or its setting issue. Concentrate on this. You also can try running only this genset and see it takes full load.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#3
In reply to #1

Re: Synchronizing panel

03/10/2009 2:53 PM

My Governor is legally blind. We exchanged a defective Governor for him. He seems to be a very good Governor but I'm not sure I'd give him an engine, no matter what transmission or tires were on it.

Ok end silliness , commence fractured English.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Anonymous Poster
#2

Re: Panels, Lines and Loads

03/10/2009 4:16 AM

You did not indicate how the load sharing system is made manually or automatically.

Is your installation provided with power return protection

How is the exitation current set?

This look like a a misfunction of the AVR mainly is there is no trip by return power.

Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#4

Re: Panels, Lines and Loads

03/12/2009 7:49 PM

Hi,

What you are seeing is circulating currents between the generators. This is a problem of your synchronisation settings. Assuming the system is working in droop mode you need to run each machine individually at no load and full load and adjust them so that they both have the same voltage droop and frequency sag at each setting. i.e. Say for example, 51 Hz 444V no load and 49Hz 430V at full load. One important thing is to use the same external good multimeter, there is no guarantee that someone hasn't misadjusted the panel meters at some time. Using the same meter means at least you are comparing "like with like"

Regards

Chas.

__________________
En la casa del herrero, cuchillos de palo!
Reply