Motor Installed Power vs. Power Input

03/11/2009 9:24 AM

Hi

can anybody tell me the difference between motor installed power (kw) & power input (kw)

what the meaning of each one

why motor number 1 installed power < power input but motor number 2 installed power > power input

which one i select c.b depend on

thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Motor Installed Power vs. Power Input

03/11/2009 2:24 PM

Can you repost the table as a larger picture, I can barely read it when magnified. All I can see is it looks like you are trying to compare a 0.25kW motor to a 30kW motor.

__________________
jack of all trades
Register to Reply
Active Contributor

Join Date: Jul 2008
Posts: 12
#2
In reply to #1

Re: Motor Installed Power vs. Power Input

03/12/2009 3:31 AM

Thanks Mr. Jack

there are tow selection EXF=0.25 & SAF=30kw

I don't compare between them but i need to now why the installed power in exf lower than power input while in saf installed power greater than power input

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4
In reply to #2

Re: Motor Installed Power vs. Power Input

03/12/2009 2:41 PM

It does look like a typo in the specification you have been given (where it says that the installed power is 30kW but the input power is 25kW). Based on the rated amps (A) of 54.7A at 400V/3ph/50Hz (which matches a standard 30kW 3ph motor) it looks like the power input (kW) should be 30kW, and the installed power should be 25kW.

Hope this clarifies the issue for you.

__________________
jack of all trades
Register to Reply
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: May 2008
Location: Placerville, CA
Posts: 80
Good Answers: 8
#3

Re: Motor Installed Power vs. Power Input

03/12/2009 9:15 AM

Which motor to choose? Well, the simple answer is to choose the one that is designed and sized properly for your application.

In actuality, I would choose magic motor #2. If you can get 30KW out of it by only putting in 25KW, I would go that route and start producing your own free energy.

I think there may be a typo on the specs.

__________________
ALL "electrical" failures are mechanical in nature.