Power Supply Distance in Pullbox

03/11/2009 10:22 PM

How to maintain distance of 2 power supply in one pullbox. Is it correct to to enter 2 power supply in one pullbox considering I used the body fill calculation on NEC Art.314?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Power Supply Distance in Pullbox

03/12/2009 9:21 AM

Depends...

The following is based on Canadian code...

Note: This reply was based on your first question, that question appears to have been deleted.

If the source of the 220v feed is from the same source as the 440v feed, as in one half of a 440v center tapped winding on a transformer, then yes. If not... then no. In short, they must be from the same "system".

There are ways of accomplishing this when the conductors are from separate systems, but, it requires a metal barrier in the raceway or other protective means such as cable armour between the conductors. See CEC rule 12-904(2) for provisions that would allow this practice.

Now... generally speaking, when it comes to such matters, the CEC and NEC are pretty much in sync with each other. Having said that... why not call the AHJ in your region for guidance. Believe me... they would rather answer your questions upfront then deal with it afterwards.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Associate

Join Date: Feb 2009
Posts: 47
Good Answers: 2
#2

Re: Power Supply Distance in Pullbox

03/12/2009 11:12 PM

Please define your use of "power supply". If simply talking about 2 different voltages, like 24 volts and 120 volts in same conduit, all conductors must have the voltage rating of the highest voltage in the conduit (120 volts). Are you talking about a Feeder(s) to a building? To a subpanel(s)? The fill requirements are irrelevant, and must be observed regardless.

Please clarify your question.

__________________
"I See" said the carpenter as he picked up his hammer and saw.
Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#3

Re: Power Supply Distance in Pullbox

03/13/2009 4:23 AM

If I understand well you need to distribute two power lines and are planning to use the same pull box.

After all it is bad practice and prohibited by several local and international regulation.

If you do, they must be completely separated in the box and clearly marked to which system they belong. And you need to adapt the drawings and get the system approved before you go live.

Yearly several maintenance persons die due this type of bricolage. They look on the plan, decide that they should cut a certain system when opening that box and inside they find more than should be. While trying to find out which cable they should cut they get electrocuted as they assumed that the power was switched off (they did themself so why checking again?).

__________________
"Here we are now, entertain us"
Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#4

Re: Power Supply Distance in Pullbox

03/13/2009 7:32 AM

North of 60 is correct. The US requires the same.

Also all conductor insulation must be the same voltage rating and do not mix un-fused conductors with fused (protected) conductors. Also you must meet all wire bending radius and conduit entry for minimum pullbox sizing in NEC 314.28

If you are using a physical barrier to separate conductors, remember you have to meet all the requirements of 314 in each section since it becomes two boxes in one.

Register to Reply
Participant

Join Date: Mar 2009
Posts: 4
#5
In reply to #4

Re: Power Supply Distance in Pullbox

03/16/2009 9:15 PM

Thanks for the reply.they are inserted in different conduits but after meeting the standartd distance of laying,I just install 1 pull box with the correct calculation based on NEC 314.28.It happens that inside the pullbox,it had a certain gap based on what I calculated using the standard calculation of NEC 314.28.Pls. verify.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#6
In reply to #5

Re: Power Supply Distance in Pullbox

03/17/2009 8:51 AM

If I saw this done this way on a job I inspected, in Canada, I would have to reject it.

A "pullbox" is considered a raceway under the code and how you have installed the conductors in it, is not code compliant.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Associate

Join Date: Feb 2009
Posts: 47
Good Answers: 2
#7

Re: Power Supply Distance in Pullbox

03/17/2009 9:45 AM

Are you a licensed electrical contrator, or working for a licensed electrical contractor? If you are, check with the local AHJ.

If not either, you are violating the law by performing work without a license.

I cannot provide any furthur instructions till I know your status, to do so would be complicity.

__________________
"I See" said the carpenter as he picked up his hammer and saw.