Thermocouple Inputs for Control

03/12/2009 4:32 AM

Hi All , I am new to the instrumentation field , in our DCS (Yokogawa CS 1000 ) i find that for control loops the temperature inputs from thermocouple are converted and are fed to AI cards instead of T/c input cards. Why is it done so.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Thermocouple inputs for control application

03/12/2009 8:01 AM

Please check these T/C input cards are Multiplexing cards or not. I think these cards are multiplexing cards & so does not continuously tracks the field values. In case mV from thermocouples converted to 4-20 ma & taken as analog input, system can get continuous values & so can be used for more reliable control.

Reply Score 1 for Good Answer
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Thermocouple Inputs for Control

03/12/2009 10:16 AM

Milliamp current signals are almost bomb-proof: in principle, what goes into the cable comes out the other end exactly the same.

The same cannot be said for a millivolt thermocouple signal, which really don't want to be sent over any significant distance. All sorts of heavy industrial stuff will interfere with them, including radio, soggy earth connections and electromagnetic/VSD/motor emissions. So, it is wise convert to a resilient signal, like milliamps, at the earliest opportunity.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 2)
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#3

Re: Thermocouple Inputs for Control

03/13/2009 1:06 AM

Hi there,

As stated mA signals are not as succint to interference as mV signals. Another factor is the cost of the compensating wire. It is far more expensive than normal instrument cable.

Another factor to take into account is the the two junctions (hot and cold) of the thermocouple - preferabely you would to try and minimilize the distance between the two as you can induce more error the longer they are.

Regards,

Craig

Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: Thermocouple Inputs for Control

03/13/2009 9:49 AM

Another aspect you should consider becomes apparent when you consider what makes a thermocouple. A thermocouple happens when any two dissimilar metals touch. The small voltage created at this junction, tracks very linearly with temperature. Naturally different metal combinations produce different voltages for a given temperature. So wire A and wire B are fused together to make a thermocouple. Now wire A and wire B must get terminated a another terminal block made of another metal C. Now instead of one thermocouple made of an AB junction, you have three thermocouples in series when you include the AC and BC junctions. So, metal C gets chosen to produce the tiniest of thermocouple voltages with both metals A and B. Once a common metal carries this signal, a quick examination of transitions to other common metals shows pairs of thermocouple voltages that cancel each other, preserving the original voltage generated by the AB junction.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#5

Re: Thermocouple Inputs for Control

03/13/2009 7:22 PM
  1. Design engineer's personal preference.
  2. Lower installation costs. (depending on length of signal cable & Z/I Device used)
  3. Less chance of induced noise in the measured signal. (the longer the cable/wiring length, the higher the chance of noise impingement on the mV signal)
  4. Better resolution and manipulation of the measured signal for higher control accuracy.

All this being said, I have worked on several systems wherein the TC's report directly to TC input cards and they work very well if the wiring is routed correctly, is properly protected, and is terminated correctly. (properly sized, properly shielded, one-end, single point cable drain attachments to ground)

Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); craigza (1); PWSlack (1); redfred (1); SHOCKISCAN (1)

Previous in Forum: instrumentation hand book   Next in Forum: hi

Advertisement